Basically because
1667 ohms = 50v / 0.03A
Where 50v is considered the `safe touch voltage` (could alternatively be 25v for more demanding requirements)
& 0.030A (30mA) is the I^n (the tripping current) of the RCD protecting the circuit.
So above equation would permit a Zs upto max of 1667 ohms & still achieve disconnection via RCD before voltage rose above considered dangerous level of 50 volts
As suggested, any & all line to earth faults in a TT will be cleared by residual current device as the earth fault path has too high an impedance (typically) to achieve required disconnection times via fuses/MCBs (or disconnection atall - check out your PEFC
)
So, for TT, MCBs provide overcurrent protection only.
In TN systems we do interest ourselves in achieving low enough Zs for the breaker to trip on line to earth faults, as this is considered our primary `Fault Protection` & the backup of an RCD is considered `Additional Protection` - even tho any functioning 30mA would
always trip before the MCB.
So when a low impedance suppliers earth is provided, fuses/MCBs offer both overcurrent & earth fault protection...
whereas with TT, the fuses/MCBs give overcurrent whilst the RCD takes over earth fault protection
Hope thats clear enough for you