D
davidjones89
Test readings on ground source heat pump are showing R1 + R2 as 0.03 ohms, zs reading taken at rotary isolator for the pump is 0.27 ohms. Protective device is a 63A type d mcb, run of cable is approx 7 metres, wired in 16mm t & e, ze is 0.11 ohms, max for a type d is 0.15 ohms so i'm well over but how come given all the other readings. Advice needed please :banghead: :icon9: