Morning Guys,
Ive done a Zs test on an outside light which is on its own circuit and am getting a reading of 35.8 ohms on no trip mode. Im using a fluke 1653 multimeter which im new to.
In the bottom of the display below the Zs reading, its displaying Ik 7A. My Ze is 75.4 ohms.
Am I correct in using the formula Zs x Ia must be smaller than or equal to the Line Voltage to earth.
which would be 35.8 x 7 = 250.6V
Its a TT installation
Ive done a Zs test on an outside light which is on its own circuit and am getting a reading of 35.8 ohms on no trip mode. Im using a fluke 1653 multimeter which im new to.
In the bottom of the display below the Zs reading, its displaying Ik 7A. My Ze is 75.4 ohms.
Am I correct in using the formula Zs x Ia must be smaller than or equal to the Line Voltage to earth.
which would be 35.8 x 7 = 250.6V
Its a TT installation
Last edited: