NICEIC visit the other day… pulled up on length of RM circuit …. Zs 1.30 ohms… RCBO 32amp B type…thoughts on this
 
Anything odd about the end-end values? I.e. high r2 w.r.t. ratio from r1 or rN, or indicating a very long length?

If it is RCD protected and just an unfortunate combination of high, but reasonable, TN-S case Ze and long, but sane from VD point of view, RFC installation then it is not an installation fault and still meets ADS.

I might be tempted to put in 20A RCBO or whatever if RCD old and unlikely to get much client testing.
 
If the circuit was too long (>106m for a 2.5mm2 ring), it might not meet voltage drop requirements.

If the circuit had loose connections, then this would be a problem for obvious reasons.

If the Ze was unusually high, then this would indicate a problem with the installation earthing.

However, if the only issue is that the Zs exceeds that for the OCPD, then there is no problem. It's a compliant circuit, as the disconnection times are met by the RCD.
 
Was it a circuit you completely installed or did you extend it?

We're trying to work out if it is high due to sub-optimal design (and everything terminated correctly etc.) or high due to mis-adventure and the DIY pixies having played.
If you tell us the breakdown of the tests, Ze, r1, rn, r2, R1+R2 it would help.
 
Circuit too long according to OSG…resistance’s on conductors high due to length… how many RM are going to be over the length OSG…suggest’s….
A bit more info as requested by @timhoward would help.

Dropping the OCPD to 25A is a "fix" only in the sense the Zs, and (probably) VD figure allowed, become consistent with the circuit implemented. But it is not really satisfactory as such a long RFC suggests it is something like a whole house on one circuit, and so total load would be high and might make 25A trip-prone.

Is there any point where you could break the RFC and link up two more cables as legs to make two RFCs? Taking great care of course not to have them cross-linked!
 
Was it a circuit you completely installed or did you extend it?

We're trying to work out if it is high due to sub-optimal design (and everything terminated correctly etc.) or high due to mis-adventure and the DIY pixies having played.
If you tell us the breakdown of the tests, Ze, r1, rn, r2, R1+R2 it would help.
ze 0.34 R1 1.12 Rn 1.13 R1+ R2 0.76zs1.00…r2 1.96
 
Last edited:
A bit more info as requested by @timhoward would help.

Dropping the OCPD to 25A is a "fix" only in the sense the Zs, and (probably) VD figure allowed, become consistent with the circuit implemented. But it is not really satisfactory as such a long RFC suggests it is something like a whole house on one circuit, and so total load would be high and might make 25A trip-prone.

Is there any point where you could break the RFC and link up two more cables as legs to make two RFCs? Taking great care of course not to have them cross-linked!
There are 3 RM in the house… this RM travels a distance from the DB before looping into the power points….in most cases being RCD protected this would not be flagged up
 
What are people's thoughts on adding a parallel 4mm separate CPC to the first point in each direction? Mathematically that would probably get the Zs under the bar. Do regs allow that?
 

Reply to Zs on ring main high in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

  • Question
Hi, it turned out to be a very corroded socket outlet, and not a ring. It was two radials. An EICR had been carried out.
Replies
7
Views
1K
  • Question
Thanks for all your input guys. It seems to be that it’s down to personal preference on the best thing to do/if it’s appropriate. In my head I...
2
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top