Please accept my apologies if this is in the wrong category, and also my ignorance as I feel I should know this but I think the heat has confused me. In the theoretical scenario where you are doing an EICR on an RCD protected circuit, but the Zs for that circuit is actually (just, say) out of spec, how would you record it? And would you fail it?? Personally, I think it is obviously a fail, but with what code? Now, I am aware that the RCD is there for additional protection, and that it should not be relied on, and that the earth fault path should ensure the protective device does what it should, and obviously if there were no RCD it would be a code 2 (please correct me if wrong here). But is there sufficient justification to issue a code X on an RCD protected installation? I am referring to TN systems here, but does the 1667 max Zs for a TT have a bearing on this?

Tin hat out of cupboard......
 
Not having an RCD isn't always a code in the first place. It depends on the age of the installation and the method of installation. Personally although a circuit that has a Zs higher than the 1.15 would not be a fail straight off, you should still ask yourself why the readings are high and if you can bring the reading down by checking terminations etc. Your tests should be pointing you in the direction of what could be giving you a high ohms reading. I've always been told that codes are the opinion of the person doing the EICR and you are in the best place to determine the codes.
 
Not having an RCD isn't always a code in the first place. It depends on the age of the installation and the method of installation. Personally although a circuit that has a Zs higher than the 1.15 would not be a fail straight off, you should still ask yourself why the readings are high and if you can bring the reading down by checking terminations etc. Your tests should be pointing you in the direction of what could be giving you a high ohms reading. I've always been told that codes are the opinion of the person doing the EICR and you are in the best place to determine the codes.
I get all that. Not having an RCD at all is no reason to fail anything as you say, provided it was installed when they were not a requirement. And I also get that it would be highly advisable to investigate why Zs is high, but, I was coming from the angle of failing it and recommending that remedial work may be required, bearing in mind the tester may not be the guy doing any remedial work. There could be many reasons for the Zs being high of course. My gut feeling would be to get it sorted and bring Zs into spec - but, what if some clever clogs customer/second opinion spark cited the fact that because it is RCD protected the circuit can't be failed?? Could you reasonable expect the customer to shell out to fix something that theoretically might not need fixing?? Again, personally, I know that I would recommend that it is sorted out every time, but what I was getting at is what code would you fail it with, if any???
 
If they are within permitted readings then I'm not sure I would give it a C2. I would be informing the customer that you are not happy with it and your reasons why. Apart from the readings have you found anything that would give you doubts about the integrity of the circuit? Grommets, earth sleeve, exposed conductors, junction boxes etc? The more you can add to your case the better.

I would just record the readings and put a note against it. Personally I would be telling the customer it needs further investigation to be able to give an honest report.
 
Some food for thought... This has been lifted from the ESC best practice guide on EICR reporting and is used as an example of a C2.

• Earth fault loop impedance value greater than
that required for operation of the protective
device within the time prescribed in the version
of BS 7671/IET Wiring Regulations current at
the time of installation

A Zs value outside of the permitted values would simply not disconnect within the permitted time, therefore being potentially dangerous. The 1667 value would not have been relevant in all probability when the circuit was installed so has no bearing on your report.
I myself would be happy coding it as a C2 and would investigate if necessary and if instructed to. I wouldn't be going round trying to solve to fault if I had no prior arrangement with the customer though.
 
Some food for thought... This has been lifted from the ESC best practice guide on EICR reporting and is used as an example of a C2.

• Earth fault loop impedance value greater than
that required for operation of the protective
device within the time prescribed in the version
of BS 7671/IET Wiring Regulations current at
the time of installation

A Zs value outside of the permitted values would simply not disconnect within the permitted time, therefore being potentially dangerous. The 1667 value would not have been relevant in all probability when the circuit was installed so has no bearing on your report.
I myself would be happy coding it as a C2 and would investigate if necessary and if instructed to. I wouldn't be going round trying to solve to fault if I had no prior arrangement with the customer though.

Exactly. I am coming at this from a purely hypothetical viewpoint, with no view to fixing anything, just reporting. If it was an install that was pre-RCD, then it's a fail C2, defo. But if there is an RCD, is it just a recommendation, ie a C3 then?? That is the point I am getting at. Or do we take it that the RCD is additional protection (not to be relied on?) and that it should be failed as a C2??? Personally, I am going down the road of a C3, but is this correct???
 
I've just read my reply here, and I think it's a bit wrong. This is a C2 yes?? Irrespective of RCD or not?
 
but, malcolm, if it was installed to s previous edition of the regs. where RCDs were not specified as being suitable for fault protection, surely it would be a C2?
 
but, malcolm, if it was installed to s previous edition of the regs. where RCDs were not specified as being suitable for fault protection, surely it would be a C2?
ohh nice one Tel. Surely if the RCD is additional protection, it should be disregarded under these circumstances?? What if it fails, then you are back to 16th ed safety considerations.....??
 
Pretty much irrelevant because that is the fault protection device there now Tel. We can only test on what is the condition of the installation now, not why a protection device has been changed. Obviously if it was an RCBO and the cable was not sufficently sized for the overload side then you need to code it
 
Pretty much irrelevant because that is the fault protection device there now Tel. We can only test on what is the condition of the installation now, not why a protection device has been changed. Obviously if it was an RCBO and the cable was not sufficently sized for the overload side then you need to code it

So in other words then, unless it exceeds 1667 ohms, the Zs figure is irrelevant if an RCD is protecting the circuit??? Can't be right surely??
 
Lets say your hypo question concerns an external lighting circuit connected in a ring main. Now some bright spark to win the contract works out that he needs a 6mm SWA and 250mts of it x price. But after calcs he can wire it in 4mm or even 2.5mm saving a fair bit but though VD is ok Zs on the cable is slightly to high what is the options open to him. Price for a larger cable and loose the contract or use a protective device that will give him his disconnect time for the cable size
 

Reply to Zs out of spec on an RCD protected circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Usually if there are only C3 observations it would usually be deemed satisfactory but could be found to be unsatisfactory in unusual...
Replies
15
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top