When testing its always been said that its important to take your Continuity reading (R1+R2) and that Zs can be calculated (avoiding working live)
So how many of you do all your correct R1+R2 values and then claculate there Zs and put this figure down on your test sheets?
Or are most of you doing both test all of the time on every install you do and recording what you get on the cert?
I know measured values will usually be slightly different to calculated values due to parralel earth paths etc..
If i take R1+R2 reading and then take my Zs reading from the same point on the circuit they very rarely calculate out write using my Ze.
Todays example..
Lighting pendant.
Ze = 0.22
R1+R2 = 1.94
Zs = 0.82
So how many of you do all your correct R1+R2 values and then claculate there Zs and put this figure down on your test sheets?
Or are most of you doing both test all of the time on every install you do and recording what you get on the cert?
I know measured values will usually be slightly different to calculated values due to parralel earth paths etc..
If i take R1+R2 reading and then take my Zs reading from the same point on the circuit they very rarely calculate out write using my Ze.
Todays example..
Lighting pendant.
Ze = 0.22
R1+R2 = 1.94
Zs = 0.82