Just having a play with my tester at home - when I did a Zs rcd on my lighting circuit it tripped the rcd still. Is this a common issue? Happened on both lighting circuits which are on different rcds.

New build so electrics are in pretty good nick.
 
OK, chalk that down as a school boy error. Was using 2 lead method on a 3 lead test
 
The latest meggers can perform no trip loop test on 2 leads. I am not sure about metrels though.
Yeah I think that's where I'm getting confused as we use meggers at college. Just checked manual and it definitely is a 3 lead test on my metrel
 
with the older meggers, 1552/3, it's a 3 lead no trip test. if you try and do a no trip with 2 leads, the megger displays "trip" and won't give a reading.
 
with the older meggers, 1552/3, it's a 3 lead no trip test. if you try and do a no trip with 2 leads, the megger displays "trip" and won't give a reading.
Guess that's a feature the metrel lacks as it let's you test and just trips out
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Zs rcd
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
hightower,
Last reply from
hightower,
Replies
9
Views
96

Advert

Back
Top