nursa

my supervisor told me, recently, that zs readings on a tt system do not have to comply with the maximum zs figures in the regs. i have always worked to max zs figures no mater what system. whose right?
 
Your maximum permitted is 1667 ohms over 200 ohms it may be unstable NICEIC recommend 100 ohms. Remember that BS 7671 is guidance so not legally enforcable despite the fact that they will quote BS 7671 in a prosecution against you, so I treat BS7671 as a legal requirement.




Chris
 
when you test the ze the best way to get a pure reading is to remove the main earth from the cu
then test onto the end of the cable
as chris said aim to get 100-200 ohms
then replace and test zs readings these may be lower due to better earth paths through bonds etc

your .25 reading is very low and there maybe something else causing this
 
Last edited:
yup it was disconnected for test. also tested gas and earth bonds getting 0.3.and 0.29 respective. cant figure out why zs readings so high. new ccu, connections all good. havent checked every termination in property but ring, lights, cooker and single spured socket all too similar to think this is the problem.
 
Seems very strange that Zs readings are so high. You might want to check the busbar has gone into the bottom of the RCDs properly. I've been caught out with thinking it was screwed in tight and got no power. The busbar had gone in front of the screw instead.
 
Ze on TT at 0.25....not a chance.

The lowest I've ever heard of was on a job I did a while back in a quarry, we ran 120mm earth on to 9 sets of 2x14mm copper rods on a grassy bank with bentonite in the hole and we only got 4.22ohms then!

Surely your mistaken??:confused:
 

Reply to zs results on tt system in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
693
For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
379

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top