bobby101

hi guys i m doing my select assement for my company soon and i would like 2 ask if when doing an Zs test on a light radial cct would i have to test all (eg, 5 lights) in said cct to determine true reading or is doing said test on one lt acceptable..
 
If you can visually identify the final light point on the circuit then you could carry out the reading there, if not, take a couple in different areas and compare.

This information would initially be identified when carrying out R1&R2 tests? Are you doing them first?
 
If it's on an initial verication for a new circuit you would have done your R1 + R2 and so therefore you should be able to indentify the furthest point on the circuit. So if you want to measure the Zs you can do it at that point.

I would though be tempted on an assement to do it by calculation and ask him if you want to confirm it by measurement. Chances are he will say no as he most likely would not want you to live test if you had done it by calculation. Saying that it will depend on the assessor but you should be able to go straight to the furthest point
 

Reply to zs testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
I have 3rd part signed off, i think, twice. Once for an apprentice who was doing his own place, i followed NAPITs rules to the letter, checking...
2
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top