I have just tested the Zs on my ring final circuit...

i got the readings 0.25, 0.32, 0.47 and 0.52

there are more but the readings were basically between 0.25 and 0.52

Ze is 0.11 and r1+r2 is 0.35

i get the same readings either at the front or the back of the socket so with the test leads or the test lead with the 3 pin plug on the end.

i understand the parallel paths or worn accesories may effect the reading.

the lowest reading was the first socket in the ring and the highest was the furthest part of the ring...... ( have i just answered my own question there?)

oh and the highest readings are not spurs cz i have checked that too.

for some reason i was expecting the same sort of reading at all the sockets......

can anyone enlighten me please

Danny
 
your Zs readings will increase as you get further from the CU to the mid point, whicich will be the highest reading,unlike R1+R2 because the latter are cross connected when reading.
 
Thanks F for that! i had a sneaky suspicion as u can see from the original post.

ok the next thing is.... if Zs = r1+r2 +Ze

then my zs should be 0.46

my highest reading was 0.52

and parallel paths only bring the zs down not take it up
 
There are a number of factors that can influenece the Zs reading such as meter accuracy, cable connections, test lead resistance, socket outlet contact condition etc etc.

TBH, I wouldn't worry about the reading you have as it sounds fine to me.
 
thanks lenny


just the question rises . i know all the connections are tight and i tested from the back of the socket as well as the front. i just cant explain how the Zs can be higher than calculated.

the tester is calibrated as of january 11 the leads are mint condition

i knew the reading was ok i just had to ask cz i cannot explain it....

if it was less than calculated id have said yeah parallel paths but tiz not the case

Danny
 
Ze readings can vary that why I was always taught to test Ze and PFC twice one straight after the other..... Surprising the differences in value you see
 
yeah thats todo with the Cycle.

all good feedback thanks everyone...

i can have my niceid assesment relaxed now....TOMORROW!!!!
 
your only 0,06 out, id be fine with that, ive seen much bigger differences, like then man said, so many external influences effect test results, right down to the make up of the cable when ur talking such small values as 0.06
 

Reply to Zs testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top