Just taken delivery of my very own NICEIC DVD: "inspection and testing - initial verification for domestic properties" and after watching it i have a question.
In the chapter about testing for Zs on radial circuits, the NIC bod says that testing on exposed live parts is a direct contavention of the Electricity at work act section 14, there for the NIC require only a calculated Zs entering on their EIC's using Zs = Ze + (R1+R2)
is this correct? because i'd have thought testing live installations would fall within the boundaries of a "competent person"
In the chapter about testing for Zs on radial circuits, the NIC bod says that testing on exposed live parts is a direct contavention of the Electricity at work act section 14, there for the NIC require only a calculated Zs entering on their EIC's using Zs = Ze + (R1+R2)
is this correct? because i'd have thought testing live installations would fall within the boundaries of a "competent person"