Hi I was just wondering if you guys can help with this I am unsure which box to tick for high zs reading plz help
Section 5(final circuits) somewhere it says about presence and adequacy of CPC, id be coding that box. I'm assuming DPN5 cert
Agree with Telectrix what form you filling in to record a High ZS with a tick?
Surely you should be recording the actual figure, coding it and be making recommendations.
When you complete the paperwork for Initial Verification, you are signing to say that it complies with the current regs.
There is nothing to complete for a high Zs reading. There is a column on the generic schedule of test results under the heading "Test results" for entering your Zs reading, this is where you enter this result. However because this is Initial Verification, then this defect has to be corrected, and retested before the installation is put into service. 612.1 refers.
Cheers...............Howard.
Reply to Zs tick sheet query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
For a new circuit or alteration the dead tests should be done first to ensure it is safe to energise.