R
roboze
hi all :),
i just got round to testing a new build i've done, and seem to getting unusually high Zs readings.
the incoming supply is 3phase (its a big house) and ze is 0.23
all other tests are fine.
the board is wylex with individuall c-type rcbo`s
all fittings are chrome.
all circuits other than the garage (white plastic fittings) zre showing abnormally high Zs readings.
So...... could it be the rcbo`s ?
could the amount of earthed chrome contribute to it?
anyone any ideas? would much appreciate your input.
my tester is a robin multi tester on the zs test it trips the rcbo but still gets a reading.
thanks people
Rob
ps its a PME system
Calculate the zs...Ze + R1 R2. Or temporarily swap the RCBO for an mcb.......I'd calculate.
yeah think i`ll check a couple of circuits with an mcb and if ok i`ll calculate the rest, thx chaps :)
You will also find that some RCD modules put an impedance in line with the circuit as well... I remember doing a load of domestic PIR's, and finding that if I measured the earth fault loop impedance on both sides the RCD main switch I could get anything up to 0.40 ohms difference, so always worth having a look at that.
But with your Robin I don't think you'll get a decent reading anyway... (Get a Megger MFT 15 series if you can, mine have never let me down!!) ;)
Zs to high!
Thread Tags
roboze,
pevvers,