Practicing with my tester so I wanted to measure Zs on my cooker (At least I now have clean floor behind the cooker ).
The cooker is on its own M6 Type 1 - 32 A MCB. It is protected by an 80 A / 30 mA RCD. I have tested the RCD and it is functioning correctly (x0.5=NO TRIP / x1=27ms / x5=11.1ms). The RCD does not trip when either the cooker or socket are in normal use.
My cooker is wired to an isolator with a socket outlet, then down to the cooker connection accessory.
If I take Zs at the socket outlet using the no-trip setting it reads 0.22Ω
However, if I try and take Zs from the cooker connection accessory the RCD trips out?
I haven't done any other tests. I know sometimes RCDs can trip even on no-trip setting but this puzzled me as the socket is OK.
What am I doing wrong?