Testing a ring final ..ze = 0.22
.r1 + r2 =0.65...
R2 +rn = 0.69
So calculated zs = 0.87
But when I test at sockets they are around 1.47
 
Testing a ring final ..ze = 0.22
.r1 + r2 =0.65...
R2 +rn = 0.69
So calculated zs = 0.87
But when I test at sockets they are around 1.47

Don't know what happened to my last post so here goes again, your r1+r2 result, is that the figure of eight result? ( R1+R2)
Losing it big time here the result of 1.47 ohms is that the average of all the sockets? or is it from one particular socket which could be a spur?
 
Don't know what happened to my last post so here goes again, your r1+r2 result, is that the figure of eight result? ( R1+R2)
Losing it big time here the result of 1.47 ohms is that the average of all the sockets? or is it from one particular socket which could be a spur?

Yes to the figure of eight and yes it was the average sockets were reading between 1.43 and 1.5
 
That is a little hard to understand Scott as, like the others have said, you've mixed up lower and upper case.

I find if anything when measured at sockets it can be 'less' then Ze + (R1+R2) due to Main bonding. Have you measured with a plug in tester? If so, it may be a good idea to use someones elses tester to see if you get the same results, or perhaps take the socket off and test actually on the conductors.
 
Last edited:
Yes to the figure of eight and yes it was the average sockets were reading between 1.43 and 1.5

In that case scott, your Zs was 1.5 I'm afraid :sick:. It's just gone up by another 0.03!
 
Testing Zs via a plug top lead can always give you false values even on new installs and why i rarely if ever use them. Test at the sockets terminals if you want accurate values that aren't relying on what is, just a scraping plug top connection..
 
Are you testing on the no trip setting on your meter? In practice this rarely gives accurate results....usually higher than the actual value. I had this discussion with Megger after I found that my meter gave wildly variable results on successive tests on the same point.Their reply was that accuracy isnt that important on the no trip setting as the RCD means much higher values are acceptable anyway!!. Renders the no trip setting a little pointless IMO.
 
Agree with Wirepuller re the no trip!

Also when using the No Trip 15mA setting you can with certain RCD's get unusually high ZS readings due to the internals of the device.

Alarmbells should start ringing if the results are not what you expect and a futher bit of investigation work is needed to see if there is a problem!

Bypass the RCD and ZS the circuit from the DB using the 25A high current ZS test if in doubt!
 
Agree with Wirepuller re the no trip!

Also when using the No Trip 15mA setting you can with certain RCD's get unusually high ZS readings due to the internals of the device.

Alarmbells should start ringing if the results are not what you expect and a futher bit of investigation work is needed to see if there is a problem!

Bypass the RCD and ZS the circuit from the DB using the 25A high current ZS test if in doubt!

This is going to start one of those debates....

It is exactly,what a competent tester could consider,as part of his investigation,but is frowned upon,by some assessors and instructors.

I reckon it is part of simplifying the instruction process,or one of a number of other reasons.

I have had this from trainers,and read this in many testing instructional books,but cannot see the difference between this "bypassing" and other bypass procedures,such as disconnecting bonding,for the purpose of a specific test.

One assessor i spoke to,concerning this anomaly,told me eventually "...well,bonding is one conductor,and one terminal..." and that bypassing any RCD,was "more involved..."

...Maybe it's just the same feeling of frustration,older dudes have,on finding some grads dissertation got a 1:1,with a spelling mistake on every other line,"coz,the content trumped it..." :icon12:
 

Reply to zs unexpected results in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
265
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top