knighty45

I did a periodic and got some strange zs values. Can anybody explain these readings for me.
Ze 14.1
Ring main r1 0.53 rn 0.53 r2 0.80 so r1+r2 = 0.33 measured zs came up with 30.3
Another ring main with very similar readings
Lighting circuit ZS was 14.4 which is more like what I would expect to see.
Thanks
 
no trip setting on mft inaccurate? as this setting only fires 15mA through the loop, a slightly high resistance connection can throw your readings out.
 
I would say that there is a poor connection at the breaker, either the conductors are not seated well in the terminal, the MCB is not properly connected to the bus bar or there is a 'high' resistance through the mcb.
 

Reply to ZS values on TT system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
706
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top