Evening everyone,
I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs column.
However, speaking with a friend he informed me that this is wrong as Zs = Ze + (R1+R2) and not (R1 + RN) which is right and never crossed my mind.
All of my work is in-house commercial maintenance so when testing for Zs, L-PE is usually lower than L-N because of the parallel paths. Only on some circuits with a smaller Csa CPC, then the L-PE is higher.
Just wanted to know other peoples thoughts on the matter?? Am I recording the wrong results??
In the terms of safety, if the circuit max Zs value passes the highest of the two readings then happy days anyway.
I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs column.
However, speaking with a friend he informed me that this is wrong as Zs = Ze + (R1+R2) and not (R1 + RN) which is right and never crossed my mind.
All of my work is in-house commercial maintenance so when testing for Zs, L-PE is usually lower than L-N because of the parallel paths. Only on some circuits with a smaller Csa CPC, then the L-PE is higher.
Just wanted to know other peoples thoughts on the matter?? Am I recording the wrong results??
In the terms of safety, if the circuit max Zs value passes the highest of the two readings then happy days anyway.