To clarify this is how I understand it:-

If the Zs meets disconnection period spec, then it will trip the CB within the alloted time period when a Live to Earth fault occurs (eg: 0.4s). However, if it can't meet it, then there must be additional protection from an RCD, to eliminate the risk of the earth becoming live because of a high ZE. This is the basic TT protection mode.

For normal ADS without RCD protection, the disconnection time is of course mandatory.
 
There's a big difference between a TN and a TT system!! The use of an RCD on a TN system is for ''additional protection'', It' shouldn't always be considered a cure all, for covering a wiring circuit that doesn't comply with required Zs when it can quite easily be made to comply. Whereas, on a TT system, especially in UK, it is the prime and only protection for earth faults

The use of RCD devices for cure all situations seems to be, becoming the norm in the UK. Get the fundamentals right first, before applying RCD additional protection
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

the pict

Mentor
-
Joined
Location
Brodick
Business Name
Devlin Maguire Electrical

Thread Information

Title
Zs what if
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
16

Thread Tags

Advert

Thread statistics

Created
the pict,
Last reply from
Engineer54,
Replies
16
Views
2,836

Advert

Back
Top