To clarify this is how I understand it:-
If the Zs meets disconnection period spec, then it will trip the CB within the alloted time period when a Live to Earth fault occurs (eg: 0.4s). However, if it can't meet it, then there must be additional protection from an RCD, to eliminate the risk of the earth becoming live because of a high ZE. This is the basic TT protection mode.
For normal ADS without RCD protection, the disconnection time is of course mandatory.
If the Zs meets disconnection period spec, then it will trip the CB within the alloted time period when a Live to Earth fault occurs (eg: 0.4s). However, if it can't meet it, then there must be additional protection from an RCD, to eliminate the risk of the earth becoming live because of a high ZE. This is the basic TT protection mode.
For normal ADS without RCD protection, the disconnection time is of course mandatory.