I have a TNCS system in my ten year old house. I have a distribution circuit running to my detached garage 4 metres away via SWA. The PME is not exported to the garage but it has a separate TT system. My question is:
How is ZS measured at the DB in the garage and how can I check the earth fault loop (Ze) is OK via the TT system? I am aware there is only one Ze and that's at the origin (CU in house). I would normally measure Ze via line and the disconnected earthing conductor. If there is only one "real" Ze at the origin, how is the TT earthing loop checked?
ZS for the db circuit would surely be L/N to the armoured CPC which of course would not be connected at the garage DB but terminated in an appropriate gland in the garage CU but would still be accessible as a CPC for the measurements?
Apologies if this does not make much sense but it is driving me mad.
Thanks in anticipation.
PP
How is ZS measured at the DB in the garage and how can I check the earth fault loop (Ze) is OK via the TT system? I am aware there is only one Ze and that's at the origin (CU in house). I would normally measure Ze via line and the disconnected earthing conductor. If there is only one "real" Ze at the origin, how is the TT earthing loop checked?