ab1978

when we measure zs on a circuit and then calculate to back up result using above formula do you get sometimes a different result to your measured zs using earth fault loop meter?
results are within the guides but can be .10ohms - or+ or more out?
 
I had a strange thing with zs readings today.
The system was a TT and the ZE reading was 24 ohms, r1/r2 was 0.3 but measured zs was 29 ohms, apparently the RCD can cause this
 
when we measure zs on a circuit and then calculate to back up result using above formula do you get sometimes a different result to your measured zs using earth fault loop meter?
results are within the guides but can be .10ohms - or+ or more out?

Nothing unusual about this - so long as your measured Zs` are lower that is!
Parallel paths back to earth often reduce a calculated reading to a lower, measured figure. Otherwise, temperature variations can alter your readings either way.
Providing your numbers are within Max Zs allowed then all fine & dandy, so don`t be tempted to adjust back to what Ze + ( R1+R2) works it out to be - `doctored` readings are obvious to a overviewer...:eek:
If your measured readings are ok, then they`re ok. Period :)
 
Last edited by a moderator:
Nobody has mentioned contact resistance yet. Or the difference between a DLock measurement and a straight measurement.

I can't actually remember the last time my figures added up.
 
Sure, you`ll always get skewed readings on a `No Trip` setting or similiar methods to keep the RCD in. They`ll increase your Zs readings by varying degrees.

As you re-affirmed tho, measured v calculated are often not that close - & the main point is not to try to get them to add up - by all means do the equation to check measured value makes sense, but if it does then have confidence in your test gear & record the result it gave you.
 
I had a strange thing with zs readings today.
The system was a TT and the ZE reading was 24 ohms, r1/r2 was 0.3 but measured zs was 29 ohms, apparently the RCD can cause this

You also need to be aware that both Zs measured and Ze measured are perfromed using mains Ac voltage at current upto 25A D lock and 15mA notrip, where as the r1+r2 are measured using a dc tester whose output voltage is 4v to 24V at only 200mA as a result trying to add an AC result and a d.c result will result in an error/difference in reading.
 

Reply to zs=ze+r1+r2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top