Hi guys, doing bit of revision here. What is the correct answer to give under exam conditions to this question? State why Ze-Zr cannot be used to accurately determine the value of R1 + R2? Could it be something to do with number of connections within the circuit under test, possibly a loose connection etc which would then give a higher Zs reading? I'm sure there must be a more obvious answer. Thanks
 
Hi guys, doing bit of revision here. What is the correct answer to give under exam conditions to this question? State why Ze-Zr cannot be used to accurately determine the value of R1 + R2? Could it be something to do with number of connections within the circuit under test, possibly a loose connection etc which would then give a higher Zs reading? I'm sure there must be a more obvious answer. Thanks


What's Zr when it's a home?
 
Driverman

parallel paths can make an enormous difference to the final Zs. The difference of an order if the Ze is appalling (which it often is, TT wise).

so for example, you may get a Zs of 6.4 Ohms for a circuit with a Ze of 122 Ohms and an R1+R2 of 0.67 Ohms.

how could Zs - Ze ever be a useful measurement, except in how useless it might be....do you see from the example above?

the bonds to the water pipe and gas pipe in the example above massively reduce the Zs.


In fact, some properties that are TT can happen to be connected via a water main to another nearby property that is TN.... Thus producing even more incredulous results (like a Ze at the earth rod of say, 34 Ohms but the socket circuit reads 0.34 Ohms for its Zs).

s.
 

Reply to Zs - Ze in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
757
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
347

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top