The sequence of testing is for safety reason, so I would say not as you need to verify the earth path you are testing is back to the earth of the DB being tested
 
I'm assuming with the OP asking Zs he actually means R1 + R2 and not r1 +r2 and on a EICR why do you need to do R1 + R2 readings to get a Zs
 
You can put as little or as much information down as you like, As long as the reasons why are included. This must be accepted by the client which is why page 1 includes this information but why would you want to not do half the testing.
 
There could be quite a lot of reasons you can not take an R1 + R2 reading on a EICR

Unable to isolate a circuit in a commercial/ industrial environment
Hi Bay lighting circuit
Safety Services

They spring to mind in a few seconds. So again there is no reason you need to do a R1 + R2 test on an EICR to record a Zs value
 
There could be quite a lot of reasons you can not take an R1 + R2 reading on a EICR

Unable to isolate a circuit in a commercial/ industrial environment
Hi Bay lighting circuit
Safety Services

They spring to mind in a few seconds. So again there is no reason you need to do a R1 + R2 test on an EICR to record a Zs value

Totally see where your coming from but if site conditions dictate you cant obtain R1 + R2 then you would have to clarify you cant obtain your Zs
 
Surely if you can measure Ze at board (or obtain by enquiry), but as you say for some reason can't turn off to do dead testing, you can still measure your Zs at the outlets which you do live anyway.
Then, assuming that's good, (R1 + R2) = Zs - Ze.
If you're allowed to put one figure down obtained 'by calculation' why not another? As long as you state that.
 
Surely if you can measure Ze at board (or obtain by enquiry), but as you say for some reason can't turn off to do dead testing, you can still measure your Zs at the outlets which you do live anyway.
Then, assuming that's good, (R1 + R2) = Zs - Ze.
If you're allowed to put one figure down obtained 'by calculation' why not another? As long as you state that.

Sounds right, but in GN3 they state you cant rework that figure with that calc, would be to easy but with all the paralel paths as it is a live circuit with bonds in place
 
If you have a previous PIR or cert available when carrying out a EICR,and that cert gives R1+R2 and Zs readings,there really is no need to carry out further R1+R2 tests,which can be time consuming and disruptive. If your Zs test results are identical or at least close to the results on the previous cert,it is reasonable to assume the R1+R2 readings will be the same as well......obviously this approach should be explained on the new cert.
 
What exactly does knowing the value of R1+ R2 achieve?
There's no requirement in the Regulations, to measure or record it.
A Zs test is quite enough.
 
taking Zs without doing an R1 R2 would mean carrying out a live test without proving cpc exixts.

Dont shoot me mr.Nic made the statement, you can calculate ZS but not R1 R2
 
We sort of touched on this on the other thread. It would really depend on the agreement from the person ordering the test with regards to isolation for testing, the less of the test carried out then the less value the results are worth which is why it must be agreed first. I think the best way to explain would be to give an example of a poor result but still obtaining a good reading.

A 4mm radial circuit on a 32A MCB with many outlets that cannot be turned off as has a computer fed from one of the sockets there is also a fused spur controlling a boiler wired in 0.5mm flex fed from this circuit. At the the CU the cpc for this circuit has become disconected but a reading of Zs on this circuit is recorded as 0.35ohms which is well within a max for MCB.
Now this circuit could turn out to potentially dangerous if a fault to earth occured on it only having a 0.5mm conection to earth with the pipework on the boiler which is why the Zs only reading is worthless.
 
taking Zs without doing an R1 R2 would mean carrying out a live test without proving cpc exixts.

Dont shoot me mr.Nic made the statement, you can calculate ZS but not R1 R2

True on a new install...but the OP is referring to a PIR,which is already energised.
 
This thread links in to exactly what im doing at the moment, EICR on commercial shops in an Airport. Over 30 boards, not one can be isolated. Some have Ze and PFC recorded from previous Reports so this.can.be recorded but next.to that all i can do is Zs and the occasional RCD test. I can whip the board open to check all connections but nothing more! Very very limited EICR but its all stated and agreed with the person ordering the report. Limited to what can be told about the system.
Sent from my GT-I9100 using Tapatalk
 
I find this to be quite interesting. We have comments regarding why this and why that. Posts about what can happen or what could happen if that occurred or this was to be, when the bottom line is, an EICR is a report on the installation, not a fault finding exercise.

R1 + R2 proves continuity of the CPC and polarity. totally agree with that and would of course always do it on a EIC/MEIWC, but we are talking about EICR, where continuity of your CPC can be proved by R2, which is why aids like extension poles were invented to help us when it is not feasible to take an R1+R2 reading

R1 + R2 will confirm as part of a formula your Zs reading and is vitally important for disconnection times. Great for initial verification to confirm your design, but I would hope by the EICR stage this design criteria is passed.

I will say the only down to not doing the R1+R2 test is that often you can pick up loose connection with it, and by not doing it they could be missed, but in fairness on a EICR you often do IR tests at 250volt and also just L/N-E, sometimes compromise is needed, this is where your training and experience guides you.

We know the NICEIC stance on "live" working and "testing", that it is not right. Well sorry but like a lot of things in this world I don't hold with that. I want to know what the value of Zs is, when the installation is "live", when it is actually working and when people are going to be using it, not what it should be on a calculation.

In the real world there are parallel paths, and these indeed affect the results on a Zs. But great long may they do, I know that when there is a fault , the fault won't say, hold on that is not fair, I'm going to disconnect quicker because of these paths, disconnect yourself please and let me have a chance to do damage!!!!!

You are reporting on the installations condition, it's suitability for continued use. Great in the classroom and the guides to say these are the tests and this is it. But also remember the same GN 3 tells us, as the inspector WE decide what tests are to be done on an EICR. If I measured 0.25 ohms on a 32amp MCB, and proved there was a CPC by the R2 method at each point, then I would not be knocking myself apart saying but what is the R1+R2
 
bear in miond also that BS7671 does allow us to use extraneous metalwork as CPC, read section 543, and in particular, 543.2.1, and 543.2.6.
This a regulation that is very very rarely used, and i think if it were to be, a lot of testers would fail it, even though it is a satisfactory method of providing a CPC.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
ZS
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
20

Thread Tags

Advert

Thread statistics

Created
dayrider3883,
Last reply from
johnboy6083,
Replies
20
Views
3,006

Advert

Back
Top