Hi.I've got a couple of queries regarding feeder pillars on a car park I an working at.
There are 3 pillars.All are metal.No 1 is supplied by 70mm 4 core xlpe swa.3 phase and neutral.cpc/bond is the swa.
No 2 is 25mm 4 core. And No 3 is 70mm 4 core. No 2 & 3 pillars also have water supply in a separate compartment.The installation is TN-S..I'm wondering should there be an earth bond run back to supply DB in main building or is the swa sufficient..The main buildings neutral is 150mm (ish) and the main bonds inside the building are 50mm.
 
Hi.I've got a couple of queries regarding feeder pillars on a car park I an working at.
There are 3 pillars.All are metal.No 1 is supplied by 70mm 4 core xlpe swa.3 phase and neutral.cpc/bond is the swa.
No 2 is 25mm 4 core. And No 3 is 70mm 4 core. No 2 & 3 pillars also have water supply in a separate compartment.The installation is TN-S..I'm wondering should there be an earth bond run back to supply DB in main building or is the swa sufficient..The main buildings neutral is 150mm (ish) and the main bonds inside the building are 50mm.
Who has ownership of these Feeder Pillars? if it's the DNO then that will be their problem not yours, adding anything to them may result in you getting a testiculating. I see where you are coming from though, to be honest I'm not sure of the answer.
 
Thanks Pete.Not DNO.
Private.I was wondering do I treat them as if they were a detached building..The 2 metal boxes (feeder pillars) have 6mm bonds to water and 10mm to frame
 
Thanks Pete.Not DNO.
Private.I was wondering do I treat them as if they were a detached building..The 2 metal boxes (feeder pillars) have 6mm bonds to water and 10mm to frame
Not sure of what you are asking "mrloy99, are you doing any work/testing in the FPs?
 
Not sure of what you are asking "mrloy99, are you doing any work/testing in the FPs?
I'm testing only.What I am trying to ask is-is the swa of the cable supplying the FPs sufficient to act as main bonding or maybe they aren't main bonds and only supplementary bonding is sufficient?
 
Tns is different from tncs,so you may be ok,Swa May be sufficient for cpc & main earth bonding.
50mm earth bond may be the bug bear there,would of been great to duplicate at pillar end.
This kinda thing is always a constant pain,the more we get to know,the more this undesirable occurs.
 
I'm testing only.What I am trying to ask is-is the swa of the cable supplying the FPs sufficient to act as main bonding or maybe they aren't main bonds and only supplementary bonding is sufficient?
The Feeder Pillars I have worked on, relied on the sheath, be it SWA or some other armouring (not sure it was a long time ago) as the main earth conductor, you would need to look at SWA data to find out the CSA of the armour and then decide, if it's large enough in CSA to act as a Main Earth and a Bonding conductor, Atatched table is all the info I have, may help.
 

Attachments

  • SWA CPC.pdf
    991.5 KB · Views: 12
For TN-S the bonding would not need to exceed 25.0, the armour of all cables is inadequate to support 25.0 bonding. What size is the earthing conductor at the source of supply.
 
The Feeder Pillars I have worked on, relied on the sheath, be it SWA or some other armouring (not sure it was a long time ago) as the main earth conductor, you would need to look at SWA data to find out the CSA of the armour and then decide, if it's large enough in CSA to act as a Main Earth and a Bonding conductor, Atatched table is all the info I have, may help.
Thanks
 
Is the water pipe metal or plastic.
Hi.The water pipe comes out of the ground in plasic then changes to copper after the stopcock then about 2 foot later terminates in a garden type tap...all inside the enclosure.
I suppose what I'm trying to figure out is if it is an extraneous conductive part..(dont think so.)is it exposed conductive part (doubt it)so then it doesnt require equipotential bonding..If it was copper coming out of the ground it would be different.(I don't know now if it even needs the 6mm)
The other item is the cabinet itself I suppose it could become live under fault conditions but should it need an additional bond in addition to the CPC?? I cant think why it would.
Thanks for your thoughts
 
Hi.The water pipe comes out of the ground in plasic then changes to copper after the stopcock then about 2 foot later terminates in a garden type tap...all inside the enclosure.
I suppose what I'm trying to figure out is if it is an extraneous conductive part..(dont think so.)is it exposed conductive part (doubt it)so then it doesnt require equipotential bonding..If it was copper coming out of the ground it would be different.(I don't know now if it even needs the 6mm)
The other item is the cabinet itself I suppose it could become live under fault conditions but should it need an additional bond in addition to the CPC?? I cant think why it would.
Thanks for your thoughts
you should never rely on using the armoured wiring has a CPC.
specially 3 phase .
 

Reply to Feeder pillar query in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top