Hi, I kinda think I know the answer to this but will ask opinion anyway. I am fitting a new compressor pump and motor to my receiver and have bought;
twin cylinder pump;
3hp motor (2.2kw)
Although, the motor looks like this
So, I upgraded the ring main that the compressor will use in my workshop to 32 amp, I'm told it can take up to 40amp with no issue, but thought I'd put in a 32amp fuse for now and try it.
Now the confusing part is, machine mart sell compressors with exactly this setup on but only require a 13amp plug. Here. or this.
Spoke to my brother who is proficient in wiring and he said to put in a separate switch, so I went for a cooker switch, the same as my lathe. (which is on a separate circuit), but he checked with a wiring expert he knows and was told I should use a direct on line starter with a motor that big on single phase. Well, machine mart sell them for £45 here
Been reading about owners of these compressors and they do not have a problem triping. Most use normal 13amp plug! which would concern me.
I'm not a heavy user, I'm a hobby user, so it will not be running every day, just the odd weekend. I guess, a professional electrician would immediately go the super safe route and insist on a starter fitted, and I don't blame them. But I can't help feel it unnecessary.
so I'm holding off for now and will take these steps as I build the part.
1) fit the 32 amp fuse and cooker switch and try it out when I first build it. Guessing the worse that could happen is that it trips out every time I use it. Then step 2.
2) Order the DOL starter (10-16amp) and fit that in place of the cooker switch I already have.
A third option could be to replace the 32 amp with a type of slower trip. My brother mentioned this is possible. I have bought this, but apparently there is a circuit breaker that won't trip immediately. Bearing in mind this is from a separate board from my house.
So, anyone have any thoughts on this?
Regards
Simon
A DOL starter provides precise overload protection for the motor and provides a no-volt release.
The wiring regulations require that a motor of this size must have a starter or device offering similar protections.
The 32A fuse will not provide adequate protection to the motor, under overload conditions the motor will burn out and be damaged before the fuse operates. The overload relay in a DOL starter however, if correctly set, will disconnect the motor before damage occurs from overload.
OK, that's interesting. Why don't machine mart tell you this or explain or even sell a DOL with the compressors they sell? I understand their pro compressors but their standard compressors with relatively small tanks still have a 3 hp motor and you wheel them around and plug them into a 3 pin socket! That part of it makes no sense.
Because they are a shop selling things, they exist to take your money, they are not a wiring regulations advice service.
If it is sold with a 13A plug on it then it may well already incorporate the necessary protection, but since you have stated that yours connects to a 32A supply it is unlikely to be the same as those supplied with a 13A plug fitted
Something I've just found when reading through the manuals of the Clarkes compressors.
Manual here
Firstly, on page 5 it states a 3pin plug.
Secondly, on page 11, it shows a reset switch on the motor. I have the same motor but I do not have that overload built in. There is instead, a blank plastic thread screw in place and nothing behind. Maybe, when they build their motors they fit an overload. Odd that they sell this as the same motor used on this compressor but there is no overload. That makes me think more that I should have the DOL starter.
the wheel round types if fitted with a uk plug as supplied, should have been designed and built with overload protection suitable for the motor and load connected.
this may in fact be the plug fuse.
because the compressor you have purchased is sold without a control system, you are responsible for designing and building something that meets requirements.
things to consider are
overload protection
over temperature protection
over pressure protection
behaviour in event of loss and restoration of power.
Edit:
Just re read the original post.
if I understand correctly,
you have bought a compressor (without motor)
a compressed air receiver
a single phase motor.
Putting all theses separate components together, makes you a machine builder and with that,
YOU ARE RESPONSABLE for the safe design and construction of the machine.
overload protection
Edit:
You are absolutely right. My situation is a working compressor with a small motor/pump. I am upgrading. I have the correct pressure release valves in the system to prevent over pressure, I have a pressure release also for when the motor starts to reduce load etc. It's the supply end that I am more concerned about. So a lot of the safety features I already have in place. My concerns are the effect of the motor starting and causing damage and why the compressors they sell do not need (or maybe they do), a DOL starter.
That said, the comment from 'davesparks', makes a lot of sense. I should be thinking about protecting my motor. So I think with that in mind, I might go immediately for a DOL starter from the off. I guess the short spike in amperage is enough to damage the motor over time. So I might go for this. I am assuming the rating 10-16amp, should match the motor, in this case 10/12 amp.
The ready-built 3hp compressor will definitely have some kind of overload protection. It might be the thermal protector in the motor as you mention the button, or a direct-acting overload relay built into the pressure switch, but there will be something. It will have been tested as a unit and certified as compliant. When you buy a bare motor, it's your job to marry it up with suitable overload protection.
The main risk and reason for a thermal overload relay as used in a starter is that long, low overloads will set a motor on fire without blowing a fuse or tripping an MCB. Or, put another way, if you were to fit a fuse or circuit breaker that protects closely enough to prevent overheating, it would trip on starting. The thermal device has characteristics that match the thermal behaviour of a motor and allow for the fitting of a larger OCPD for short-circuit protection only, that will handle the starting current.
The 3hp 14cfm compressor that you link states that it requires a 30A supply, not 13A. However they are a bit wobbly on the motor specifics; there is a figure of 2250 watts but this is the mechanical output power, it's a direct conversion of 3hp. The electrical input, which you would expect to see given as a line current or (as it's a complete appliance rather than a bare motor) a power consumption, is not stated.
OK, so fitting a thermal overload into the box where there seems to be space for one is a good idea. Would you recomend a device?
I've seen this.
I've ordered the DoL starter, a thermal reset switch appears a relative low cost and simple item to fit, I assume I run the live through the switch and if it runs at a high amperage for a period of time it will trip, in the case of the one linked above, at 15amp, which is higher than the 10/12a usage but lower than the 32amp trip. Or will it trip on startup and act like a fuse? A little advice on this would be appreciated.
To reiterate the safety of my build
My build has;
One way valve into tank
0 load valve, so the motor will start with no compressed air pressure in the head
Auto switch off at preset pressure
Tank pressure tested and steel thickness measured
Overpressure valve on tank and in line with feed to tank from pump.
I'm adding;
32amp supply with isolator
Direct on line starter (ordered)
Things I have yet to add but working it out;
Guard for belt/fan/dangerous spinning bits
Thermal overload (when I figure out which one to buy)
Things I may not add.
Any device to deal with power cut as the motor will be protected by a trip, DOL starter and would not matter anyway as the motor switches off at pre set pressure....unless the DOL does that anyway.
Cheers for comments and help so far.
the direct on line contactor should come with or you should fit the correct sized overload for the motor it's controlling. You should not have any need for that that thermal overload switch as well.
I'm assuming your current set up would start the compressor automatically as the pressure drops bellow as cetain threshold? This should be run through the controls for the starter so a simple DOL starter will not work as you require it.
I don't quite understand everything you say there.
You say the DOL Starter I'm getting should have a thermal overload switch?
this is the one I'm getting
So I could check that out.
The confusing bit you say is that the DOL will not work as I require. I run the switch for the motor from the pressure sensor, then that sensor is powered from the DOL. When the pressure drops, the pressure switch powers the motor. the pressure switch will be live as long as the DOL starter is switched on.
That starter has an overload relay inside which can be set between 10-16A.
With the DOL starter you have selected stop/start of the motor is controlled by pushing the buttons on the front of the starter. Your set up should have the pressure switch stopping and starting the motor via the DOL contactor and overload the pressure switch should not have the motor running current through it.
So you are saying, I should have power going to the DOL, then to the pressure switch, back to the DOL then the motor. That really does not make any sense to me. Is that what you mean? In other words, the last thing before the motor should be the DOL?
If that is the case, then I should mount the DOL onto the frame of the compressor.
[automerge]1588251408[/automerge]
Maybe if I put power through to the pressure switch, then to the starter, then the motor. But then, when the pressure switch wants to start the compressor again will the DOL reset to off? Or will it stay on?
I can't stop to answer fully but there is confusion going on between a starter with a contactor i.e. relay, which is controlled by the pressure switch and takes the motor load itself, and a mechanically latching pushbutton switch with thermal overload which is what I think is in the link. The latter is normal for compressors of this size where the pressure switch is rated for the motor current, since the electrical latching of a contactor isn't needed and can't be used if under pressure switch control.
the starter is a big switch designed to take the motor current what operates this big switch is a little switch, in your case the pressure switch.
If you're not clear on how to connect them up correctly why not ask your brothers mate to have a look. Or just buy a prebuilt unit big enough for what you need. Try Atlas Copco they make good compressors with everything built in.
I have asked exactly that to be sure I get the best I can. Sure, I can spend over £1k for a built unit that has a receiver this size but I would rather renovate my 1960 classic compressor tank to suit everything else in my garage for £300.
I'm not using it for professional usage, it's for now and then and I suppose I could buy a cheap smaller compressor for less and save my time learning, but when this one is finished (and I'm in no hurry), it'll see me out. Plus, I enjoy the small challenge.
I'm rebuilding a classic car in between, so it's a nice distraction during this lock down period.
But thanks to all for the advice so far, I'm slowing going up the right path. I'll post a picture when it's done.
What car are you working on?
Singer Gazelle. Nothing exotic, but a good work horse practical classic. Finished a ton of welding with her, she is now in patchy grey primer here and there, but the crap all-in-one compressor that was bolted to my receiver was just not up to the job of spraying. So I'm upgrading that, it will look more original with a twin cylinder on top. Just renovated an old 2 post lift that I got for a favour, it was rusty as hell but now smells of grease and hammerite. I recently learned a lot about hydrolic lifts and can now lift the old girl up to work on her. It's the same with that, I could have spent a couple of grand on a lift, but would rather spend the evenings figuring it out myself and trying to fix something that is fundamentally better quality.
My mistake miss read the original post and got mixed up thinking you were using a 32A motor. I don't think you will need that DOL starter and overload relay if the pressure switch is a decent one that's rated for 16A you could just use a 2 pole motor protection circuit breaker. These are suitable for motor disconnection as well as overload protection.
I was advised to use the starter as it will pull a lot when it kicks in. Question is, where do I put it in the supply, before pump or on wall going into the pressure switch.
Not sure what consumer unit you have or if you have spares ways in it but some of them will fit in there if not buy a small housing for switched O/L. I'll PM you some links for the bits when I've finished feeding the family !
fired it up today whilst I await the DOL, works very well. Would like to post a picture but apparently jpg is not recognised so I can't be bothered to figure that out.
The lights flick slightly when it fires up, but I have not run her for a long time yet until I fit the starter.
So, eventually the starter turned up. Meanwhile, been getting mixed messages form various people, most staying, you don't need a starter for that!
But I've got it and fitted now so tough, I have one.
I can't tell the difference with it fitted, maybe it seem to start slightly less aggressively, which, if true, is a good thing.
I'd like to share a picture of it but apparently a 'jpg' is not an image as expected!
But overall, i've repainted the compressor, added a dump valve so the cylinder heads do not have pressure when the motor starts, a one way valve, rebuilt the pressure switch and 3d printed a new cover for it, turned up a new button to switch it on and off, obviously fitted a new pump and motor, all new connector hoses and high temperature hose for the pump to receiver and starter with overload protection set to 10 amp currently. (that's adjustable)...oh and a crap oven isolator which I'm going to send back. I can't believe such a low quality switch could be sold.
Only one frustration in all this. (short rant coming up, I apologise)
1) Strip, sand clean receiver and asy; 2hrs
2) paint, 30mins
3) fit pump and motor, drill new holes, align pullies etc; 1hr
4) fit new regulators and air gadgets to compressor; 20mins
5) fit electrical boxes to wall; 10 mins
6) Align flat head screwdriver to godforsaken retarded, out-of-date, frustratingly irritating, dumb---- flat head screws that all electrical fittings seem to have; 600000000days
Why, for crying out loud, why flat heads? come on, there must be a logical reason to use these? I mean , Philips are so much quicker and easier and secure! It just beggars belief. I curse when I come across the odd one in my 1965 classic car, but all electrical fittings have this crappy screw head that I forever have to fiddle around trying align my screwdriver to, then slip off and swear as I faf around looking for it again. Wiring up took 100x longer than it should have, it's not hard, just stupid. I designed a cover and sent it to my 3d printer quicker than I could do up all the frikin stupid screws on the electrical fittings. Even the ones that hold the front cover on are stupid flat heads.
Rant over, again, I apologise.
Thanks for all your help here.
I know, just a pet hate. Same with Philips, torx and any other head type, but flat is simply anoying.
forum is having problems with uploading pics. what you can do is either upload as a pdf, or send pic. to image host site, then post a link to it.
As already explained, a motor starter has a specific job to deal with: to allow motor start surges while also protecting against motor overload, where as the supply MCB or HRC fuse is there to protect the starter from massive fault currents.
You won't notice a good starter doing its job, but without one if the motor is locked or otherwise overloaded you will find a burned out motor which costs a bit more to replace than the starter costs!
Whatever you choose to do in life, never even contemplate becoming an organ-builder.
Reply to Compressor 3hp motor DOL starter question in the Electricians' Talk area at ElectriciansForums.net