There multiple ways or doing it. Maintained or non maintained? And are they dedicated emergency fittings or combined? Is this a college question?
Conceptually it's just like having two light switches for two groups of lights. A normal switch for the normal lights. And a key switch for the emergency lights that is usually 'on'.
The main thing wiring-wise is that maintained lights (which are on all the time) can be wired from any lighting circuit or their own circuit.
Non-Maintained lights are not on all the time, so the supply needs to be common to the normal lighting in the areas they are protecting. e.g. If lighting circuit 1 trips, then the emergency lights in the rooms that now have no lights need to come on.
Thanks for the reply.
Predominantly non-maintained fittings. And most of the fittings are dedicated, for example EM bulkheads and spots in open plan areas, corridors etc. Not a college question, but I may have to install some soon.
Thanks Tim. Much appreciated.
The buildings which I'll be looking after non- maintained for the most part. So take for example room 1 general lighting. I install NM em lights here and take feed from the same mcb feeding general lighting in room 1.
From Mcb to 6A control mcb- onto my CTU, which in turn, would feed the NC terminal of a contactor if there were a large number of lights on the circuit?
In that case probably a dedicated circuit(s) from board to contactor and then out to lights, switched by a key switch or timed switch for testing purposes. Or if no master switch then local switches in areas for testing.
A typical LED non-maintained unit consumes about 3-4 watts. The older T5 bulb units are more like 20W. How many units are we talking about?
To be clear, you are suggesting the contact0r coil is powered by the local lighting, right? As it's non-maintained fittings.
It would be a master switch. So in terms of the wiring of it, supply from board ie for eg.10A mcb to the CTU or key switch, then onto contactor and from there out to circuit?
Reply to Emergency lighting diagram? in the UK Electrical Forum area at ElectriciansForums.net
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Hi folks, Can anyone recommend a reliable brand for emergency lighting bulkheads please? I have a job coming up to replace 30 odd units. I have...
Hello Got a customer who needs certification for a monthly emergency lighting test. What would be the best cert to provide them with? The NICEIC...
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...