S
Sparks13
Hi all,
I was sent to a job the other day to put in a supply for a new 3-phase motor. Our projects department decided instead of installing a new circuit from the DB which was situated 10 metres away wanted me to cut an existing three phase 32A SWA supply, feeding another motor and install a junction box to spur off of this supply to feed the motor.
Now personally I don't agree with this set up of spuring off single/3phase (with the exception of lighting and ring mains where BS7671 allows), especially as the junction box was hidden within a service duct. Now I am not too sure as to how this corresponds with BS7671...
Have you guys got any comments as I'm not too sure where I stand with refusing to do works that don't comply with the conventional set-up.
Many thanks,
Peter
I was sent to a job the other day to put in a supply for a new 3-phase motor. Our projects department decided instead of installing a new circuit from the DB which was situated 10 metres away wanted me to cut an existing three phase 32A SWA supply, feeding another motor and install a junction box to spur off of this supply to feed the motor.
Now personally I don't agree with this set up of spuring off single/3phase (with the exception of lighting and ring mains where BS7671 allows), especially as the junction box was hidden within a service duct. Now I am not too sure as to how this corresponds with BS7671...
Have you guys got any comments as I'm not too sure where I stand with refusing to do works that don't comply with the conventional set-up.
Many thanks,
Peter