Hi everyone,

I would really appreciate some advise. I'm a domestic electrician but my neighbors asked me for some help on a issue he has and here I am.

So my neighbor has a tree surgeon company, they have a yard where the cut and dry logs as well. So they've just got a new drying system installed and have a new 20KVA generator to power the yard. A few weeks ago the generator started spewing oil, the manufactures said it's because the generator is be under loaded, so they said they should ideally run the generator at 12KVA to be most efficient.

I went to the yard today and the supply is 3-phase. I measure the current drawn on each phases as L1:4.4amps - L2:0.4amps - L3-1.0amps

Total loading 5.8amps. If I put this into KVA I get 4.0KVA on 230v and 5.8KVA on 400v.

I worked out 12KVA to be around 17.3amps

Any if the above i correct or am I completely wrong somewhere. Also any advise on the best way to increase the loading, the yard is ran 24/7 and is in constant us. I was thinking of a dummy load, but wanted to get other opinions or ideas! I've attached a pic or 2 of the generator and controls.

Any advise is welcome.

IMG_7746.JPG


IMG_7747.JPG
 
Not sure how you got those numbers!
5.8*230 = 1.3kVA
I'd agree that a 20kVA genny is likely to gunk up if run for long periods with only 1.3kVA load*, as the engine will run cool, with bore glazing, ring sticking etc. as a result. There's a difference between peak efficiency and minimum continuous load though - I don't think you need to load to 12kVA to keep it happy! A dummy load will simply waste fuel however, and he is already wasting fuel by running a set of that size for 1300W of load.

It sounds like the genny is far too large, but one would have to know what the normal and peak loads are for the installation. Any info on this? If they have a heavy load when sawing etc. but a light 24-hour load for the drying fans, that would suggest getting a small genny for the 24-hour load only.

*Strictly, as far as the engine is concerned, it's the real power (kW) load that matters, but it's fine to work with kVA as the power factor probably won't be that far from unity.
 
Last edited:
If the set is spewing oil, there is something fundamentally wrong.
The light load you have across the three phases will not make it do this.
As a rule, with any three phase generator, you should aim to balance the phases as evenly as you can and it's not a bad thing to ballast the load with halogen floodlights or heaters to ensure there is always some demand on each phase, although doing this to 55% of its rating seems excessive and will waste fuel.
Thisparticular set is rated 22kVA or 17.4kW, so across the three phases will be good for around 25A per phase at 230V
 
Thanks for the replies. This is definitely not my usual field.

When I went there today they informed me the usage it was using at the time was the same it would us literally 24/7. As the boiler consumption is wood chipping and literally the only additional use is a arm which move chipping in to the furnace from time to time, light loads.

The generator only feeds the containers and all other machinery, everything else chainsaws etc... are petrol powered.

They've just spent ÂŁ6k on the generator as their electrician who wired it up informed them they required a 20KVA generator.

I think there trying their best to use the generator they've purchased as otherwise it's money down the drain.
 
I just wanted to check my measurements, so I simply held a clamp meter on L1, L2 and L3 to measure the current being drawn. Out if curiousity how do you work out the KVA, is it simply the KW rating of what's being drawn.
 
I just wanted to check my measurements, so I simply held a clamp meter on L1, L2 and L3 to measure the current being drawn. Out if curiousity how do you work out the KVA, is it simply the KW rating of what's being drawn.

Your profile says you’ve completed the 2330, but you don’t know power calculations? This was definitely a part of the 2330 course when I did it.
 
I can’t see how the poor loading would cause oil to spew out of the generator. However being under loaded and out of balance is not going to be doing it any favours!

The only time I’ve seen a generator spew out oil was when the hire company sent one out to us without the dipstick in the engine.
Shortly after starting it it started to run a bit rough, I opened the access door to see oil spewing out of the dipstick tube!
 
it's been around 10years and mainly I just do House bashing, and maintence etc.... and I haven't done 3-phase since my early years.

I'm guessing you would add up all machinery/loads etc.... in KWs and divide by .8 to get KVA. Does it work the same on 3 phase?

I'm not posting on here to start a ----ing war, was just after some general advice in a field I don't specify or work in.
 

Reply to Advise needed. Diesel generator loading issues in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Another one that some of you may be interested in.......... We had a call to remove 4 off blackstone generators from a pumping station in south...
Replies
3
Views
1K
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
So, very long story short.......I got given a bit of a generator, free if you take it out! All sounds too good to be true and it was, they got...
Replies
15
Views
1K
Hi All, During my exercises on paper, we always assume the source from grid has Tension and Currentnin phase. Today, for the first time, I was...
Replies
5
Views
2K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock