Hi there hope you can shed some light.
Ive got a cooker rated at 3.5kw
A hob at 6.4 kw

Now if i look to apply diversity to this to run a single T and E to a cooker switch the from the switch to a click double cooker connection point.


is this correct?

3.5kw =15.2 A
6.4KW = 27.8 A
TOTAL = 43 A

With diversity applied I'm looking at 10a + 30% of 43a = 22.9 a

Cable run 18 m Clipped direct therefore 6mm to cooker isolator

Any advice is greatly appreciated.
 
where's that in the regs ( green book)?

edit. even so, 6mm on a 32A MCB , you're stilll well in. have you calculated the VD?
 
Last edited:
Diversity for cookers takes into account the cyclical nature of the loads within that particular appliance and their co-ordination with each other. Where you have two separate appliances there will be no co-ordination between these appliances so I would tend to carry out a diversity calc for each appliance and then total.
You must also reference the manufacturer's information provided in case there are any requirements for cable type and size.
Also your cable size choice does not seem to have a bearing on your calculation.
 
1db75291fab030898fd2a7255d5b69af.jpg


This is what mine says.
 
Diversity for cookers takes into account the cyclical nature of the loads within that particular appliance and their co-ordination with each other. Where you have two separate appliances there will be no co-ordination between these appliances so I would tend to carry out a diversity calc for each appliance and then total.
You must also reference the manufacturer's information provided in case there are any requirements for cable type and size.
Also your cable size choice does not seem to have a bearing on your calculation.

Nonsense, it works just as well across multiple appliances as a single appliance. Each element in a single appliance is individually controlled exactly the same as if they were all in seperate appliances.

I had a fish and chip van at a festival last year, the total load of cooking appliances plus some downlights and fluorescents was 15KW, I worked happily on a 32A supply. My data logger recorded a max of ~30A whilst it was fully in use.
 
Ha Hha I've been trying to do that lol

so "It is in the on site guide and the wording is 'the first 10A of the rated current plus 30% of the remainder of the rated current'"

i take it as 10a plays the full load not the first 10a then remaining?

 
K your the man andy lol my baddd!!!! ha ha

so what cable size are you stating and how would you calculate it differently
is this now correct

3.5kw =15.2 A
6.4KW = 27.8 A
TOTAL = 43 A

With diversity applied I'm looking at 10a + 30% of 33a = 19.9 a
 
Nonsense, it works just as well across multiple appliances as a single appliance. Each element in a single appliance is individually controlled exactly the same as if they were all in seperate appliances.

I had a fish and chip van at a festival last year, the total load of cooking appliances plus some downlights and fluorescents was 15KW, I worked happily on a 32A supply. My data logger recorded a max of ~30A whilst it was fully in use.

I have also clamp tested cheap electric hobs that allow near the stated full load current to be drawn. Not a very common occurrence I will admit, but I'll stick to what I said.
 
what would you say then Resu??
Baring in mind I am technically still a trainee...

Minimum cable size would actually be 2.5mm although you wouldn't find a circuit breaker to suit! Common sense says 6mm though, seeing as you are running a new circuit in anyway. This would future proof too (to a certain degree).
 
In a new kitchen scenario with plenty of sockets I never use a cooker isolator with a socket, I don't think 5 amps is a very realistic assumption although something like a 'fast boil' 3kW kettle would admittedly only be on for short periods, I just think it's better to keep the cooker circuit purely for the cooker.
 
Baring in mind I am technically still a trainee...

Minimum cable size would actually be 2.5mm although you wouldn't find a circuit breaker to suit! Common sense says 6mm though, seeing as you are running a new circuit in anyway. This would future proof too (to a certain degree).

2.5mm on a 25A MCB? then Ib<In<Iz, so circuit complies.
 

Reply to Applying diversity to Cooker unit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock