Because a diyer/trainee reading that statement may well believe that they can export pme to any outbuilding without any special requirements, which isn't true.

They, or anyone else, cannot 'export' PME to any outbuilding. They can however extend an PME equipotential zone to any outbuilding (except those falling under specific circumstances)
 
They, or anyone else, cannot 'export' PME to any outbuilding. They can however extend an PME equipotential zone to any outbuilding (except those falling under specific circumstances)

There’s no regulation that says you can’t export a PME earth to another building.
 
There’s no regulation that says you can’t export a PME earth to another building.
I think a lot of the confusion surrounding this comes from the word 'export'. It only crops up in these conversations, and doesn't seem to exist in any set of regulations that I'm aware of.

What does it mean? Does it mean extending the separated earth, from the MET, to the outbuilding (generally acceptable), or does it mean extending the combined neutral/earth to the outbuilding (not acceptable)? DNOs almost certainly will tell you that you can't do the latter.
 
What is of interest is whether there is selectivity between the two RCDs. Why is there a 100mA upfront on a TN-C-S?
I was wondering about that.

Certainly you could use a 100mA delay RCD along with something like a 50A D-curve MCB to get better selectivity with down-stream OCPD based faults and/or still meeting disconnection times on the higher resistance SWA armour to save cost going 3C.

I suspect it might just have been TT originally and in recent years the DNO made it TN-C-S?
 
how many faults per year on pme lost neutral very little the power lines are monitored ,you have got more chances of being kissed on the lips of a giraffe 🦒.
I'd like to know this too - wonder if anyone has collated such events via FOI request or similar. Since it is regularly raised as a potential risk in guides etc, I'd like to know just how often it happens so that I can make a well informed risk assessment on certain types of job.

(For avoidance of doubt, I'm talking about faults on PME, not being kissed by a giraffe 😉 )
 
I'd like to know this too - wonder if anyone has collated such events via FOI request or similar. Since it is regularly raised as a potential risk in guides etc, I'd like to know just how often it happens so that I can make a well informed risk assessment on certain types of job.
Available data getting a bit old now....
1661858442823.png



Interestingly someone tried an FOI request in Nov 2021 and HSE never responded, leading to the ICO upholding a complaint.
I can't find the results though.
 
I looked at a few of these posts then skipped to the end. Take no notice of the majority of these as they just seem as though they like to argue rather than knowing what there doing. Exporting a TNCS is fine as long as you can prove and are happy it's OK. A 100mA RCD can trip before the 30mA at x5, it shouldn't but it can. To stop this you can install a separate isolator at the mains so it doesn't come from the board in the house then run the SWA to the shed from that. Your running a sub main not a finale circuit so it does not need protecting by an RCD. If you still want the shed to be TT then terminate the SWA into a plastic adaptable box then run the correct sized earth from the stake to the shed DB.
 
default said : " Take no notice of the majority of these as they just seem as though they like to argue rather than knowing what there doing. "

But do you know what you're doing? Because I think what you're suggesting wouldn't be compliant.
 
Last edited:

Reply to Assistance with my installation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
782
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock