I've come across this incomer, looks like 10mm conductors.

The dno has upgraded the meter and used a 100A fuse.

So my question is, does this need reported or can I do whatever work I please along as I don't overload the 100A fuse 🤔
20230407_154431.jpg
 
Last edited by a moderator:
It may not be an 100A fuse inside.
The earth-clamp alone is enough reason to be talking to the DNO in my opinion.
 
What type of cable is that? Is it singles in conduit or is it MICC? With a clamp on pot for the earth? If it's MI, it might be large enough, partly because the solid conductor is larger than it looks, and partly because of its high current rating for a given size.
 
What type of cable is that? Is it singles in conduit or is it MICC? With a clamp on pot for the earth? If it's MI, it might be large enough, partly because the solid conductor is larger than it looks, and partly because of its high current rating for a given size.
I wondered if it was MICC. Would it be possible for them to be double insulated (as they stand) if it was?
 
Whatever it is, its the incoming supply cable but looks a bit DIY with the earth clamp to provide TN-S earth connection?
 
Yes looking at it again I see the female bush now. 7/.052 looks about right, just under 10 sqmm. Anybody spot the strands of earth that didn't make it into the clamp terminal?
 
It's a BS951 pipe clamp on a conduit, that obviously isn't the service cable itself but extends from either a multi-service cutout or looping point or something elsewhere.

When I first looked at it on a phone screen it looked like the end of a pot poking out but it's a female bush. Sometimes MI is used in this application between the point of entry and the meter position. Often with the pot and stub sleeves exposed; not correct practice but it is done.
 
If they are approx 10sq, the cutout fuse (up or downstream) may have been derated to 60A.
Just hope that they are ‘tails’ and not exposed singularly insulated conductors!
 

Reply to Dno incoming tails too small? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top