Currently reading:
External metering enclosure
Discuss External metering enclosure in the UK Electrical Forum area at ElectriciansForums.net
Folks
Could you suggest an fused isolator of choice, to install in a recessed external metering cubicle, in a domestic installation, this will be required to terminate a 25mm SWA
I am unsure of how much space I can utilise of the standard enclosure, not to encroach on the DNO cut-out and meter installation
seen loads of installs, done in 80's and 90's where isolators have been fitted in meter cabinets at new build stage. as long as there's room, bung one in.
Good plan, until they say OK we'll just remove our equipment from your property.
This all boils down to whether you are willing to stand your ground, and how far you are willing to take it.
The DNOs have no real grounds to refuse to allow an isolator or switchfuse in a meter cupboard.
In fact if you are willing to pay them, I bet they would be quite happy to install one for you.
Well, unfortunately the gestapo don’t allow any equipment in their enclosures apart from their own..
You will need to install an extra enclosure for your kit or have the isolator internal near enough back to back with their meter
You could get them to provide one...…..I wonder where they would put it?;)
Quick update folks
Called into DNO head office and was able to establish they would accept, an isolation device located tight against the right-hand side, but didn't confirm what space they would be willing to sacrifice, which brings me back to the original question
What switch fuse would be suitable to terminate a 3 core 25mm swa in a small footprint as the cubicle is only 400mm wide
And needs to house the DNO cut out and also
I used one of the crappy metal Lewden 100A switch fuses last time (not my choice!), fitted tight to the bottom right. The meter box was surface mounted with the armour cable sticking out the bottom, though there will be room for the cable to enter the top right of the swfuse if you need to. This left plenty of room for the cutout on the left and loads of room above for meter.
Usually, there is room top right but there is not a lot of room for bending radius for the SWA, therefore, the SWA would need to be made off and slack pushed back. I have not installed any of the new metal switch fuses but the Wylex one seems to look ok I always take into consideration room inside the switch fuse to make off and forming of the 25mm tails as they are sheathed.
Reply to External metering enclosure in the UK Electrical Forum area at ElectriciansForums.net
