Search the forum,
Discuss Hi Ze Reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
2C 16mm SWA should be 1.15 mOhm/m for R1 and 3.7mOhm/m for R2, so R1+R2 ought to be around 0.49 ohms. as @SJD says what you are seeing is a lot higher than realistically expected here so look for loose/corroded glands at the ends, or missing banjo+flying leads so it is depending on rusty/painted enclosures for the CPC.
If both ends are good and clean then it points to a more worrying aspect that it could be corroded armour underground somewhere, but that would usually take years to develop following puncture of the surrounding sheath. Also IR the cable on its own (both ends disconnected and wiped clean of any dust/damp), that might indicate water ingress somewhere if it looks low-ish.
More generally you won't get much of an improvement with an earth rod, often it is hard to get Ra below 50 ohm with most soils and that is not going to make a significant change to 2.4 ohms.
If after fixing it still is too high for the supply OCPD then fitting a delay RCD along with the MCB/fuse feeding it is another means of ensuring ADS times are mot and you still have a sporting chance of selectivity with end circuit RCD/RCBO at the annex CU.
You could use a rod and delay RCD if the armour is failing and cable otherwise OK, in effect making the annex a TT system with part of the sub-main on TN earthing (to the corroded segment) and the end of the system on TT using the rod at the annex. But you have to be able to meet ADS on the rod alone, hence the only realistic option is a 100mA or 300mA delay RCD as part of the supply protection.
Sounds a bit high a reading to be due to just the cable resistance? What is Ze at the supply origin? Perhaps poor or corroded connections of the armour?
Connections look all clean and tight with origin reading 0.16
Ins res L-E 3.37, N-E 4.27
and N-L 2.36 so not great
So should be looking at a Zs reading of 0.16+0.49 = 0.65? (when energised, but presumably this is an old unused cable) so sticking with expected R1+R2 for now should be 0.49ohms?
I could understand high L-E and N-E measurement if corroded swa at gland or similar but that shouldn't affect L-N measurement which should be about 0.23ohms! unless something amiss with cable?
Didn't you get an IR reading of 0.7M between two of the conductors?
I did. Have since gone back withnewly calibrated tester and done a new clean test. Its quite concerning that the reading is so different. The 63a mcb at origin has tripped out several times but not recently.
cable in ground approx 25 years
Do some continuity tests to establish where continuity is amiss.
R1+R2, R1+Rn, R2+Rn.
Ze o
You don't appear to be clear with the problems here.
You talk about insulation resistance of 2.36 to 4.27 - is this Mohm?
This is irrelevant to the Zs
You don't appear to know the differences between insulation resistance, Ze and Zs.
If you do have Ze of 0.16 ohm at the feed end of the cable and ~2.5 ohm at the load end, there is absolutely something wrong with the cable or terminations.
I would expect a r1 + r2 of 0.5 ohms or thereabouts.
You need to find this fault, not cover it up by adding rods or anything else.
You need to measure the r1 + r2, the r1 + rn etc. This will show if you have a cable fault. And will identify which conductor is the problem, if they all read 0.5 ohms (less for r1 + rn) then the fault is between the cable feed end and the header. - most likely a bad connection in the earth path.
Ze o
Thank you for the advice..
yes - Clearly stated
Insulation resistance
N-L 2.36 Mohm
N-E 4.27 Mohm
L-E 3.37 Mohm
Ze at origin 0.16
Load end of swa 2.42
Connections at feed end sound
Will double check load end next visit as earth clamp used on armour and not accessible yet (cupboard base being removed to access)
Will do continuity tests same time.
earth clamp on armoured? i would hope we are not talking about a BS951 earth clamp . as everyone says you have either a bad cable or bad connections .sometimes a thermal camera can help if you load the cable with an electric heater .
I squared R losses would make for some heat under load.
check for thermal damage ,could the cable be joined somewhere else?
It may be linked though, based on the information in this and the other thread about this cable. It sounds to me.like the cable is damaged underground and water is getting in, hence the variable IR results which would possibly link to the poor Zs as the armour will be rotting away nicely.
All this, and your previous thread, point towards the submain cable being damaged underground and deteriorating.
No amount of checking connections at each end or other faffing about will make it any better.
You could fully isolate that cable and test it to confirm.
If it is damaged underground then no amount of earth rods or workarounds will fix it. It needs to be either repaired or replaced.
If it has been damaged for a while then water will have got quite a long way along the cable and rotted away a lot of the armour so it's unlikely you'd be able to do simply cut out the damaged section and joint a short piece of cable in, you'd end up digging up many, many metres of it to find an unaffected but of the armour.
Agree, overall the cable may be FUBARed, however in diagnosing the high Zs the IR results don't help.
I would have spent the time finding the high resistance fault as the priority.
Once that's found, it may mean the cable needs repair/replacing anyway.
The Zs for the socket circuit is not relevant your
👍 Thank you for that.
Time to bite the bullet I think.
You test from the main earth terminal to eliminate problems between that and the cable armour if this gives problems then test to the armour. If this is an adjustable earth clamp that needs addressing anyway.
You really need to focus on the length of SWA in question. If it was me I would completely strip down all the terminations BOTH ends and also IR from both ends at 500V minimum.
Ze at origin is a good reading
Reply to Hi Ze Reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Hi all Suggestions please. I’m working on a 3 phase shop install with a bunch of typical circuits. As each cct is energised the earth leakage...