Search the forum,
Discuss How to work out no value of Zs to Ze being 0.35 ohm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi all, ive been asked this question
A direct measurement of Zs cannot be carried out. The supplier gives a Ze value of 0.35 ohm and the line and cpc resistance as 36.24 milliohm/m. If the circuit is 31metres in length the earth fault loop impedance will be?
What is the formula please?
Thank you
Are those units intended to be the same or do you mean Ze of 0.35 ohms and 36.3 milliohms/metre (maybe for 1.5mm T+E).
If that is 36.3 milliohms/metre:
The circuit's estimated R1+R2 will be 31 X 0.0363 = 1.13 ohms
Then best you can do is just add them, so 1.48 ohms.
It sounds like the supplier has just given you the max allowed TNCS value anyway.
You probably know that ignoring any parallel earth paths makes this an estimated worst possible value, assuming all connections are good.
If @Anthony Deakin returns it would be interesting to know whether this is a real situation or an exam question.
The other curious thing is that a moderator has changed the original to read 36.3 ohms per meter which is surely completely implausible. I doubt the human eye could see a wire with that resistance!
I still think it's most likely 1.5mm csa T+E , as my book has that as 36.24 milliohms / m
My bad I mis edited think I have it correct now.
Thanks guys, to be clear it was 0.35 ohm for the ze and 36.3 milliohm/m.
I’ve been told by a nerdy electrician that the correct answer is 1.475 ohm but no idea how they got to this.
cheers
Reply to How to work out no value of Zs to Ze being 0.35 ohm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Cable calcs using cable calc app Working out cable size for a workshop. 100m long, 100a supply, mccb 100a zs- 0.23 ohms, in a duct on its own...
My brain has been exercised a bit by this. Am I on the right lines with this extremely simplified example: If we take: -TNCS installation with a...
4K
i don't the exact value of the soil resistivity as no survey of soil sample is carried out at the site .However Copper earthing electrode 50mm...
Hello everyone I'm Chris. I am taking the 2391 in February. This question is from the c&g main site under 2391 sample questions. Continuity of a...
4K