A bit of an embarrassing question.

I have a regular customer who I enjoy working for. He has asked me to install an EV rapid charger for his avant loader (electric tractor type thing). I always turn down 3 phase jobs as I don't feel I understand it fully, but I'd like to do this job.

I believe this is the charger (400V/32A version) Rapid battery charger, e6 - https://www.avanttecno.com/uk/options/rapid-battery-charger-e6

I have added a picture of the 3 phase supply.

1. Are there any additional tests to do, compared with single phase? Phase rotation etc.

2. Is it simply a matter of connecting L1, L2, L3 from the Henly blocks (or perhaps the 3 phase merlin gerlin board) into whatever the instructions say is needed? (eg 30mA RCD)

3. I get a little confused by the role of the neutral in polyphase. Does the neutral have a role in 3 phase or is it simply there to support single phase appliances?

3 phase supply.jpg
3 phase supply.jpg
 
Last edited by a moderator:
1. Are there any additional tests to do, compared with single phase? Phase rotation etc.
EDIT: First point is your safe isolation test has a lot more checks (10 instead of 3)!

L1 to L2,L3,N,E
L2 to L3,N,E
L3 to N,E
N to E

You should verify phase rotation and that phases are correctly assigned all the way (i.e. L1 at the end is from L1 at the supply). Even though most electronic loads don't really care about rotation direction, it is still wrong to not get it right!

The PSCC is usually taken as twice the highest of the three L-N PSCC (on the assumption N has the same impedance as L when measured, and then under the worst-case L1-L2-L3 "bolted 3-phase fault" the virtual neutral has zero impedance).

2. Is it simply a matter of connecting L1, L2, L3 from the Henly blocks (or perhaps the 3 phase merlin gerlin board) into whatever the instructions say is needed? (eg 30mA RCD)
You will almost certainly need the N as well, and some form of OCPD (i.e. fused-switch or MCB/RCD or RCBO)

Taking it from the existing board is fine if there is space and you can get compatible RCBO for it. Ask @westward10 as he seems to know every board ever made!
3. I get a little confused by the role of the neutral in polyphase. Does the neutral have a role in 3 phase or is it simply there to support single phase appliances?
For simple loads like a 3-phase motor you may not need N as it runs off the L1-L3 lines alone.

But in most cases it is needed as there will be some loads to N for single-phase work (e.g. electronic controller for main 3-phase motor, etc), and some "3-phase" units are star-connected and not always balanced (e.g. heater with 3 setting that simply select L1, L1/L2, or L1/L2/L3) so without N the voltages are wrong and potentially dangerously so.
 
Last edited:
As per PC's post, you would definitely need the neutral on the charger as some vehicles can only actually charge on single phase, but they still use the same connector.

All chargers in vehicles tend to need the neutral as they have to be able to use a single phase supply as that might be all that's available.

Specialist vehicles such as fork lifts etc may be different.

Phase rotation won't matter, but should be done right anyhow.
 
EDIT: First point is your safe isolation test has a lot more checks (10 instead of 3)!

L1 to L2,L3,N,E
L2 to L3,N,E
L3 to N,E
N to E

You should verify phase rotation and that phases are correctly assigned all the way (i.e. L1 at the end is from L1 at the supply). Even though most electronic loads don't really care about rotation direction, it is still wrong to not get it right!

The PSCC is usually taken as twice the highest of the three L-N PSCC (on the assumption N has the same impedance as L when measured, and then under the worst-case L1-L2-L3 "bolted 3-phase fault" the virtual neutral has zero impedance).


You will almost certainly need the N as well, and some form of OCPD (i.e. fused-switch or MCB/RCD or RCBO)

Taking it from the existing board is fine if there is space and you can get compatible RCBO for it. Ask @westward10 as he seems to know every board ever made!

For simple loads like a 3-phase motor you may not need N as it runs off the L1-L3 lines alone.

But in most cases it is needed as there will be some loads to N for single-phase work (e.g. electronic controller for main 3-phase motor, etc), and some "3-phase" units are star-connected and not always balanced (e.g. heater with 3 setting that simply select L1, L1/L2, or L1/L2/L3) so without N the voltages are wrong and potentially dangerously so.

As per PC's post, you would definitely need the neutral on the charger as some vehicles can only actually charge on single phase, but they still use the same connector.

All chargers in vehicles tend to need the neutral as they have to be able to use a single phase supply as that might be all that's available.

Specialist vehicles such as fork lifts etc may be different.

Phase rotation won't matter, but should be done right anyhow.

If there are three spare ways in the Merlin board then yes take the circuit from there but you will have to fit a separate rcd as you won't get a four pole rcbo for that board.
Very glad the 3 of you posted, thanks!

A further basic question... so I would take the L1, L2, L3 from a 3 pole MCB that is in the CU (and the N from the neutral bar) to the required 4 pole RCD (or whatever the MI say to take it to). (pic of CU attached).

I'm cringing a bit asking that as I know its such a simple thing. Is it simply the same as taking a supply from a single phase CU to feed whatever it is you want to feed (I.e sub DB, item itself etc) but you have 3 lines instead?

3phase CU.jpg
 
A further basic question... so I would take the L1, L2, L3 from a 3 pole MCB that is in the CU (and the N from the neutral bar) to the required 4 pole RCD (or whatever the MI say to take it to).
Yes, just like that!
<insert Tommy Cooper gag>
I'm cringing a bit asking that as I know its such a simple thing. Is it simply the same as taking a supply from a single phase CU to feed whatever it is you want to feed (I.e sub DB, item itself etc) but you have 3 lines instead?
Mostly this is the case.

It is always better to ask if you don't know!
 
One thing that appears in the picture above is the selection of meters. Will the EV charger need to have its electric usage accounted for separately? If so you might need to put in a billing meter for it that can be used to reconcile usage with the main meter, etc.
 
One thing that appears in the picture above is the selection of meters. Will the EV charger need to have its electric usage accounted for separately? If so you might need to put in a billing meter for it that can be used to reconcile usage with the main meter, etc.
I don't think it will need it's own meter as this will be the owners tractor, I will ask him though as he has asked for meters before on other work around the place.

A 3 phase meter! More questions! 🥺

I've just thought of a bit more in relation to cable size....

Lets say this is the 400V/32A charger.

1. Does each line conductor have to be able to cope with 32A?

2. I realise we have been given 32A in this case, but if we just had the wattage of the charger (lets say 22kW), is the calculation the same as single phase. I.e 22000/400 = 55A?
 
Last edited:
Be extra careful about old and new colours! Old black and blue have exactly opposite functions to new black and blue. If a new circuit you shouldn’t hit this issue though.
IR tests - basically test every permutation.

You’ll be fine, enjoy it, and want to do more!
 
New posts

Reply to Installing a 3 phase rapid EV charger? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
336
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K
I have a single 7kW EV charger that serves three holiday cottage. The supply to it is E7, with the night rate currently at exactly half the day...
Replies
7
Views
3K
Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
969

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top