If you look at the technical information from the MCB manufacturers website you should be able to obtain the maximum cable size that the device can accommodate, I think a typical 40A mcb will accept a 25mm cable but you need to check this. You will also need to check that the neutral and earth conductors can also safely be accommodated n their respective terminals. The issue normally with larger SWA cables is having sufficient space in the enclosure to gland and terminate the cable.Is it possible to put a 16mm swa on a 40a mcb protected by an rcd
why would you think it may not be okayIs it possible to put a 16mm swa on a 40a mcb protected by an rcd
OK, what is it feeding load wise.Is it possible to put a 16mm swa on a 40a mcb protected by an rcd
and will be going on a 63a split rcd board.