Currently reading:
joining 16mm T&E
Discuss joining 16mm T&E in the Australia area at ElectriciansForums.net
B
BristolSpark
Any ideas on joining a 16mm T&E.
Its fed from a main switch up into a flat. Its mechanical sound just to short to reach new board. it needs to be joined under the floor.
But we are lost on best practice for this.
Would a 60A junction box help you? What's the rating of the cables protective device?
This supply will pop out of the floor by about 6- 8inchs max. so we could put a small enclosure then JB it. Then ininstall the new board. We have not had proper chance to view the switch, from the height we are at we assume at present 63A supply.
Running a new cable was original thought thought, but due to location and being a third floor flat, access is rather bad, the route is not easy.
If you've got 6-8 inch to play with and seen as the 16mm t+e is for your main incomer, just wall mount henly tail connectors and run your tails from them to the new board. This way you comply with 543.3.3 for testing as Murdoch pointed out.
use 16mm cable link, clamp properly and wrap with PVC tape
Welcome to the forum.
Unfortunately the member in question hasn't been active in some time and this discussion dates back to 2011. In the UK we have a few options for joining cables of this type and size, but wrapping with PVC tape would not be permitted as a suitable means of insulation and protection.
Reply to joining 16mm T&E in the Australia area at ElectriciansForums.net