I want to create a new code for that:
PI : Potentially Interesting
Pretty certain I only ever see 3 pole main switches with removable neutral link. Maybe OP or @Risteard can confirm or make me look foolish
Discuss Low insulation resistance reading in the UK Electrical Forum area at ElectriciansForums.net
You need a special switch if you want to switch 3 P and N - one where the neutral contact is set back so it closes early and breaks late, relative to the 3 phases.Pretty certain I only ever see 3 pole main switches with removable neutral link. Maybe OP or @Risteard can confirm or make me look foolish
What about if its TT earthing ?4 pole main switches are fairly common here, but the point was more about the fact we're free to use them, whereas I believe they can not be used in IE.
TT (Direct) Earthing is essentially non-existant within the State, bar perhaps a very few relics. TN-C-S (Neutralised) applies to very nearly 100% of electrical installations.What about if its TT earthing ?
should never break a neutral via a switch , if it hangs you can end up with 400 volts on a 230 volt circuit which will cause havoc.I could be wrong, but have a funny feeling that regulations in IE require that 3 pole isolation is used and neutral shouldn't be broken. Perhaps this only applies to the main isolator or perhaps it doesn't apply at all...
On a TT you need to isolate all conductors including the neutral, hence the switch where the neutral contact is set back so it closes early and breaks late, relative to the 3 phases.should never break a neutral via a switch , if it hangs you can end up with 400 volts on a 230 volt circuit which will cause havoc.
No caravan parks, swimming pools, stables etc ? That would use TT earthing ?.TT (Direct) Earthing is essentially non-existant within the State, bar perhaps a very few relics. TN-C-S (Neutralised) applies to very nearly 100% of electrical installations.