Evening all
Let’s see if anyone can solve this one.
Recently wired a new extension. Today connected up ring circuit to 32amp mcb, all relevant dead testing done ir +999mohms and ring continuity.28 .28 .48. So all good turn mcb on and pop it trips off. Rechecked testing removed sockets just to double check for any small nicks etc all fine. Reconnect and turn on all seems fine. Hour or so later same problem. Replaced mcb all fine. Hour or so later same problem. Any ideas????
FYI nothing plugged in yet so no load whatsoever
 
As you haven't mentioned RCD tripping (assuming there is one as its a ring circuit) I presume that is ok so looking for a L-N fault!
If not showing up on the meter, its a matter of elimination!
 
Hi chaps
Ir testing to its own cpc tests clear. The rcd doesn’t trip either, suggesting a short circuit but again this test is clear?? Not tested with it connected to met.
It’s a bit confusing
 
Just to clarify, you are testing the circuit with all disconnected from the 'mains'.
You connect to the mains, including cpc's to MET and the RCD does not operate but the mcb does! without any appliances connected (ie No Load).
Have you checked Ze? If within spec and if L-E fault RCD should operate. Fault current defaulting to N!
Matter of elimination!
 
Hi, my thoughts : Confirm ir is still good. Clamp the L and confirm there really is no I with circuit energised. Finally relocate circuit into an other working mcb and see if it still trips. My suspicion is there's a trapped conductor to be found.
 
Let’s see if anyone can solve this one.
Recently wired a new extension. Today connected up ring circuit to 32amp mcb, all relevant dead testing done ir +999mohms and ring continuity.28 .28 .48. So all good turn mcb on and pop it trips off. Rechecked testing removed sockets just to double check for any small nicks etc all fine. Reconnect and turn on all seems fine. Hour or so later same problem. Replaced mcb all fine. Hour or so later same problem. Any ideas????
had this before, faulty mcb .
 
Yeah that’s right no load at all( kitchen not even fitted yet)
All tests done disconnected then reconnected and the mcb trips not straightaway the last time but within a hour or two. Ze reading of 0.12 on tns. It may be possible the rcd went the last time as I was not there.
 
Yeah that’s right no load at all( kitchen not even fitted yet)
All tests done disconnected then reconnected and the mcb trips not straightaway the last time but within a hour or two. Ze reading of 0.12 on tns. It may be possible the rcd went the last time as I was not there.
change the mcb first .had one a couple of months a go .customer kept say the electric off .waited 2 hour watching the cu ,and low and behold it trip right in front of my eyes .and all circuits where covered by rcd .c**P BG, screwed fix mcb
 
Somewhere there is a line conductor touching a piece of (partially) earthed metal that is not part of the circuit cpc.
With a trip time of one hour you are looking at a current of about 40A.
Because it was instant trip initially the fault has burned this contact partially clear which is why it is now taking one hour.
So I would be looking for a point where there is metal pipework near the circuit or a metallic structural part that may have been screwed in and the screw hit the line. Then testing IR line to MET as you break down the circuit.
 
Hi chaps
Ir testing to its own cpc tests clear. The rcd doesn’t trip either, suggesting a short circuit but again this test is clear?? Not tested with it connected to met.
It’s a bit confusing
What IR tests are you doing L-N, L-E, N-E
 
Evening all
Let’s see if anyone can solve this one.
Recently wired a new extension. Today connected up ring circuit to 32amp mcb, all relevant dead testing done ir +999mohms and ring continuity.28 .28 .48. So all good turn mcb on and pop it trips off. Rechecked testing removed sockets just to double check for any small nicks etc all fine. Reconnect and turn on all seems fine. Hour or so later same problem. Replaced mcb all fine. Hour or so later same problem. Any ideas????
FYI nothing plugged in yet so no load whatsoever
Did you conduct the figure of eight test on the RFC as a matter of interest?
 
Ir test done l-n l-e n-e.
I’m going back this morning to try and solve this, my thinking at the minute is what was previously said maybe somewhere line conductor is touching metalwork/pipework through a screw or something just strange I can’t read any sort of fault through the meter (which I know is ok)
 
So after further investigation and with earths still connected to met, an ir fault between two points is present! This is only through the the fabric of the building and not end to end of the cable. With this link out all test clear again even with earths connected to met. Mcb down rated builders need to make a decision on holes in walls and ceilings down
Hopefully that’s solved
Thanks for your input chaps
 
The op is stating that his test is not identifying the problem. 240v is an rms value and the meter is only performing a low current test. OP is fault finding, a 100v test will be more onerous on the installation.

The OP had stated that the test has not identified the problem but also that the test had been carried out incorrectly, this is not the same thing as the test not showing the fault. Now he has returned and carried out the test correctly it has revealed a fault.

Yes 240V is the rms value, the peak is around 300V, this is why we test at 500V.
IR testing is a low current test at 500V or 1000V, high current is not necessary for IR testing, it is the voltage which 8s required to stress the insulation, not current.
The insulation of T&E is only rated for up to 500V and shouldn't have a voltage higher than this applied to it.
 
Just a note original ir tests were carried out with earths connected to met. This was all clear! Since then work has carried on so this is when the fault has arisen. It was only not checked again yesterday that has caused me to only find it this morning.
 
had similar. nicked L insulation in back of socket. arcing to box when faceplate screwed on. showed clear on IR test @ 500V.
 
If you have used the same batch of mcb, try and get one from somewhere else, or temporarily connect to an existing mcb as you know that one is ok as it is in use. Otherwise the problem has the symptoms of an overload despite nothing is connected. You did say it went pop first and then later reconnecting it and the it lasted an hour. So therefore it seems a wiring situation, maybe a dodgy accessory e.g socket or spur if used. On your IR test are all socket switches closed, just a thought. If you are confident in your wiring I would disconnect the accessories and then try, I know it's laborious but at least you will know. Hope this helps and please let us know the outcome as It could help me. Thanks.
 
Sounds like a cable between both points has been nailed/screwed etc catching the live and going into the fabric of the building what work has been carried out between the two points in time?
 

Reply to Mcb trips but tests clear in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a 32amp MCB for my heating (heat pump) and when the heating comes on, it trips after a few seconds. If I push it back up it works fine...
Replies
8
Views
912
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
624
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
873
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top