Mix of old and new colours for singles for same circuit

Discuss Mix of old and new colours for singles for same circuit in the UK Electrical Forum area at ElectriciansForums.net

timhoward

-
Esteemed
Arms
Supporter
Reaction score
9,012
New one for me...
Commercial building (museum), 3 phase board
16A MCB, 3 x 2.5mm singles run in 20mm conduit, ending up at an FCU. All fine.
The singles are red, blue, and yellow/green.
Red is used for L1, Blue is used for N

My gut reaction is that this is just too confusing and needs sorting.
Tiny niggling doubt is that technically each wire is a permitted colour for it's use. I can't see anything in regs about consistency of old/new colours on the same circuit.
Any thoughts one way or the other? I'm leaning heavily on "this is not ok" regs or not.
 
In the old days (pre 2004) it was common to find single phase circuits wired in SWA with red as line, yellow as cpc and blue as neutral. The fact its singles in conduit makes no real difference. As has been said, sleeve the red as brown or the blue to black and all is good.
 

Reply to Mix of old and new colours for singles for same circuit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top