Wardie
Couple of weeks ago I signed a lease on an industrial unit (all 25 units in the building are 'wired for 3-phase').
Although the unit had a single phase CU the wiring was there for 3Ph.
Spent the last week installing a 24way DB, sockets, isolators etc. etc. etc., got it all checked and certified all in time for EDF to come and change the meter.
When the guy came out he looked in the meter-room (after he'd asked if I had any meter tails as he's almost run out) he said that the building is over capacity and he can't do the meter change!
Apparently there are 32 100A fuses in 2 'Lucy Boards' (I think that's what he called them), obviously this is fine if all units are 1ph, however there are already 5 units on 3ph. When I asked to see how they had managed to install the last couple of 3ph supplies I saw that they had taken the phases from fuses already in use. He said that cannot be done so refused to do it for my install (fair enough if it's not allowed).
They are now saying that I have to arrange for the building to be inspected by the Project Gateway Dept of UK Power to see what my options are. Possibly looking at months before it's all sorted (my landlords are being great as they were under the impression that if the wiring is there for 3ph then surely all units could have it if required).
What I can't understand is the practice of using 1 fuse to supply 2 separate units a total no-no (as I was told), if so, was it acceptable about 15 years ago when the building was wired? Are there cases where this is acceptable?
I'm just desperate to get my machines running, I mentioned this to the EDF guy and he explained that I should get a Henley Block and wire the single phase into that then I can connect from that into L1, L2 and L3 on the DB and I'll have 3phase...I walked off after that!
Sorry for the long rant, just wondering what my options are.
Although the unit had a single phase CU the wiring was there for 3Ph.
Spent the last week installing a 24way DB, sockets, isolators etc. etc. etc., got it all checked and certified all in time for EDF to come and change the meter.
When the guy came out he looked in the meter-room (after he'd asked if I had any meter tails as he's almost run out) he said that the building is over capacity and he can't do the meter change!
Apparently there are 32 100A fuses in 2 'Lucy Boards' (I think that's what he called them), obviously this is fine if all units are 1ph, however there are already 5 units on 3ph. When I asked to see how they had managed to install the last couple of 3ph supplies I saw that they had taken the phases from fuses already in use. He said that cannot be done so refused to do it for my install (fair enough if it's not allowed).
They are now saying that I have to arrange for the building to be inspected by the Project Gateway Dept of UK Power to see what my options are. Possibly looking at months before it's all sorted (my landlords are being great as they were under the impression that if the wiring is there for 3ph then surely all units could have it if required).
What I can't understand is the practice of using 1 fuse to supply 2 separate units a total no-no (as I was told), if so, was it acceptable about 15 years ago when the building was wired? Are there cases where this is acceptable?
I'm just desperate to get my machines running, I mentioned this to the EDF guy and he explained that I should get a Henley Block and wire the single phase into that then I can connect from that into L1, L2 and L3 on the DB and I'll have 3phase...I walked off after that!
Sorry for the long rant, just wondering what my options are.