I’ve just done an EICR on an old 2 bed flat that is wired in all metal conduit wired in singles however there are no CPC’s. The conduits are all bushed into the old rewireable board and back boxes/conduit boxes for lights and I’m getting good Zs readings at all outlets through the sockets/lights being fixed into the back boxes/ conduit boxes. There are no fly leads from the boxes to the cpc terminal on any of the sockets/fittings as there are no fixed terminals on the back boxes due to their age. All bonding is in place and I will be upgrading the consumer unit to a new RCBO board. I’m considering putting the fact their are no CPC’s down as a C3 rather than a C2 as it was obviously compliant at the time and I’m achieving compliant Zs readings. Thoughts?
What are you questioning no cpcs to the accessory front plates or no cpcs through the conduits.
With power accessories such as socket and fuse connection outlets the cpc is important as would metal be for metal plated light switches but you have to make a judgement as to how detrimental their absence is. How are the light fittings connected to the conduit system.
Reply to No CPC’s, conduit doing it’s job, C2 or C3? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
4K
Hi all, I'm wondering if it's permitted to replace an outside wall light myself if I use the existing wiring from the old light. In theory I just...
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Hi, I’d appreciate views on the fuse board. https://ibb.co/xj0BtZt It’s been completely rewired and I’m unhappy with the quality. I’ve...
14K