Discuss Odd PME test result... in the UK Electrical Forum area at ElectriciansForums.net
Morning guys!
Went to look at a consumer unit change today with a PME supply.
Now, right next to this was an old BS3036 60A fused mem cutout that then sent a pair of 16mm tails to the consumer unit up into the loft, across about 3m and then down the wall in surface trunking down to an old Crabtree CU, with a separate 16mm main earth along side.
Did a Z test at the CU and had a 0.45ohm result, but then the PME cutout had a Ze of 0.47?
I will call the DNO to make them aware, but from what i can see, a BS3036 fuse has an ELI max of 1.07ohms so as this is all well within the limits of the installation, so surely this is ok?
I have no plans to remove the MEM unit and replace with a new one as it is in excellent condition.
Probably just a parallel path interfering at the CU but that small difference could be could be the test leads or the meter "seeing it" differently.
Your Ze is theoretically too high for a PME system.
16.0 conductors contained in trunking are undersized for protection by way of a BS3036, 60A fuse.
Thanks.
I guess i might need to swap the 3036 for a 50A MCB & enclosure
as there is currently no way to replace the tails that easily!
Reply to Odd PME test result... in the UK Electrical Forum area at ElectriciansForums.net
Hi. New to the forum. I hope I've chosen the correct category to place my post. I tested a landlords property recently, turned out to be TNC. I...
EICR: I’ve come across 30mA RCD supplying a consumer unit via a 63A MCB and 16mm T&E. connected via an isolator to the cutout PME. (Ground floor...
6K
Hi folks, first time poster and soon-to-be landlord's assistant (letting my partner's property out now that she's moved in). We've just had a new...
8K
....TN-S appears outside, butt TT employed inside. Good Evening Everybody (This is my first post) Overview: The supply to my parent's cottage...
4K
Hi, I'm a recently qualified electrician and my parents need their consumer unit replacing as they are having a new bathroom and they currently...