Hi can someone help me with this situation please.
The service head/meter is in a brick built housing box in the middle of a field, we are running power to a house some 40m away from it and im not sure of the most suitable method of protecting the 25mm SWA cable from overload. The DNO fuse is 100A and ideally would like to have 100A at the house. Can I safely use a 100A type C MCB in a small consumer unit at the origin? or is there a better way? I cant reduce the supply to 63A and go with a type B mcb as this wouldnt be sufficient.
Simon
Simon
You're stuck between a rock and a hard place with this. From a purely electrical perspective the DNO fuse provides the overload protection, however there is the fabled 3m rule which says you need to provide a CPD and some discrimination. Your quick option would be an 80A KMF, there isn't really anything between that and 100A. If you want to get as close to 100A as possible just not quite (and I'd be intrigued on a domestic, but that's another story...) then you need to look at electronic adjustable MCCB's and then you're into big money.
Off the cuff I can tell you the cable is well undersized for your needs.
You need to establish the installation method, we already have the length and cable type so you then need to apply cable calc's to establish the recommended cable size for this run to ensure your VD is compliant.
What is in this house that demands so much electric? Most properties will happily run on a 60 or 80 amp fuse without incident.
PS - is this 1ph or 3ph?
Well spotted, I didn't really look at that bit!
LOL - yeah it jumped out because (without checking) I believe its rated at 104amps surface mount meaning 40m and possibly buried might de-rate this by 40% but I will let someone else check up the figures, I'm winging the response without the tables here ?
Ok, so its buried underground, on the cable calculator I used, I admit I have forgotten all the manual calcs, 25mm came out as more than sufficient for 100a with a 2.7% VD... if buried! I am happy to be schooled on this because its been some time since school and I have never come across a situation like this.
I should add that this is a kind of temporary measure as a second house is being built on the land and the service head will be moved to the main house and a second supply put in to feed to the first house. Then we will be able to adhere to the 3m rule. ( which i thought had dropped to 1m now)
The house could survive on 80 Amps however they may want to put a kiln in it at some point. hence the higher requirement.
Reply to Overload Protection of "submain" in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...