Hi there, was at a 3 phase DB today doing an EICR with another spark, there was a 10amp mcb with 1x 1.5mm2 PVC twin clipped direct feeding 4 high bay lights via a normal 10 amp switch the other spark then got his note pad out and wrote no overload protection iam say there kind of thinking a mcb protects against overload iam still an apprentice in my last year but I thought it was strange thanks in advance guys ?
 
I can't see the issue here. The MCB is no more than the switch, and the cable is going to be at least 10A but any of the usual methods (OSG Table 7.1(ii)), in fact 16A in this case. So for me that is fully overload protected, unless the "clipped direct" cable is in a very hot environment.

If the cable is massively long then it might fail on fault protection (i.e. end of cable Zs not enough to guarantee <= 0.4s disconnection) but unless it is some weird choice like a D-curve that is going to be quite long, at least 52m for B-curve (OSG table 7.1(i) as too lazy at this point to try and compute a length-limit).
 
I can't see the issue here. The MCB is no more than the switch, and the cable is going to be at least 10A but any of the usual methods (OSG Table 7.1(ii)), in fact 16A in this case. So for me that is fully overload protected, unless the "clipped direct" cable is in a very hot environment.

If the cable is massively long then it might fail on fault protection (i.e. end of cable Zs not enough to guarantee <= 0.4s disconnection) but unless it is some weird choice like a D-curve that is going to be quite long, at least 52m for B-curve (OSG table 7.1(i) as too lazy at this point to try and compute a length-limit).
Thanks a lot mate, that answer has put me on the straight and narrow this is just for my own learning great to get a second opinion from other people ?
 

Reply to Overload protection on lighting in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top