Discuss Proving structural steel is bonded in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Carrying out some EICR on a commercial/industrial site.
Previous records state the structural steel is bonded, and visually I can see 4x 25mm Earth wires leaving the main earth bar, I cannot trace the one going to the steel , though I suspect one of these does.
How do I prove this? Is it a case of isolating all power( an operational minefield) and testing between the steel and out going 25mm earth wires?
On a second point if I may, neutrals not in order on a large 3 phase DB so I disconnected neutral link bar and tested NxE at outlet end (500v) and still got a reading at less than one ohm.
The cables are in good condition , and the breaker dosent trip when in use , so I do not think it is a dead short.
Any body any pointers on these? It may be I'm missing something simple, my head is bursting today! And any help/ is greatly appreciated .
Thanks in advance
Thanks in advance
Are you oingthis EICR as part of your apprenticeship, or on the QT for some extra dosh?
For the bonding just use a wander lead and test back to the MET.
As for the N-E fault, the MCB won't trip but an RCD would.
Are you competent to carry out periodic inspections?
wandering lead method and sometimes visual verification
(once during a christmas shutdown some copper scrounging git clipped all the bonding conductors from all the i beams) we found them missing on startup inspection and they were replaced.
Reply to Proving structural steel is bonded in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all, I would like some advice on a scenario currently at my workplace. I am replacing a Sub main DB and replacing the wiring to sockets/lights...
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
BMS installers have attended. After fitting the panel they also replaced the aged lighting in the boiler room with 6ft LED battens as instructed...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...