cliffed

-
Arms
Supporter
Reaction score
650
What code would you give for a Swa supply 3p/N,95mm.
Supplies remote school block,2 storey,no main earth conductor,using sheath,the main earth bonding originates from this Swa,for this block,@ Main Panel board,& is 16 mm
The main earth @ origin is 120mm,Main bonding 50mm.
Cheers
 
What code would you give for a Swa supply 3p/N,95mm.
Supplies remote school block,2 storey,no main earth conductor,using sheath,the main earth bonding originates from this Swa,for this block,@ Main Panel board,& is 16 mm
The main earth @ origin is 120mm,Main bonding 50mm.
Cheers
What do you mean no main earth conductor?
You’ve just stated earthing conductor is 120mm
Using the armour for a cpc is acceptable if sized correctly.
What is the earthing arrangement?
Using the armour as a combined cpc/bonding conductor could be acceptable if say it’s TNS
 
Swa ,sheath used for main earth,the 120 mm Earth is at the origin intake of the school,this Swa is a sub main,to a remote block.
Tncs is the earthing system,185 mm Tails,120 mm Main Earth,50 mm earth bond.
 
Correct a cpc,my opinion is a code 2.
A main earth should have been installed with this Swa,to provide an adequate earth,& Main earth bonding.
 
Correct a cpc,my opinion is a code 2.
A main earth should have been installed with this Swa,to provide an adequate earth,& Main earth bonding.
Your opinion is flawed unless inspection and testing revel otherwise.
Have you carried out the appropriate inspection and testing to verify that the current set up is potentially dangerous?

Again it’s a CPC not a MAIN earth

What is the earth arrangement?
Does the distribution circuit have adequate fault protection by ADS for its respective ocpd?
 
Last edited:
Yea it’s a cpc the Swa is being used for Main Earth @ the Main Panel in the block.
It’s also being used for the Main earth bonding conductor.
The situation is not potentially dangerous,what are you going on about my opinion is flawed,
The earthing is Pme Tncs.
 
Yea it’s a cpc the Swa is being used for Main Earth @ the Main Panel in the block.
It’s also being used for the Main earth bonding conductor.
The situation is not potentially dangerous,what are you going on about my opinion is flawed,
The earthing is Pme Tncs.
I mean you can’t go on opinion, only by proof that it is potentially dangerous
 

Reply to School block Swa supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, I hope you could share your experience and advice regarding supply 50 flats in 5 storey block of flats. We get 3 x 430A supply. What...
Replies
4
Views
1K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
What would of stopped this happening? Job I did this morning. SWA supply for outbuilding had sliced basic insulation at the gland due to poor...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock