D

danbadger

Hi. There is a 60 amp 3 phase supply and a company has said they will to put in a star delta motor starter (55kw) which will run a gear box(55kw) that needs to be tested i do not know if the gearbox runs at 55kw continuosly , is this possible or would it be better to run a new supply? thanks
 
As Bugsy said.....more info required?
Just to give you a bit of an idea,we have a compressor at work which has a 30kw motor on a star/delta setup and is supplied by 63amp HRC fuses motor rated to 100amp.
The supply will be too small if your connecting a 60amp 3-phase supply to a 55kw motor....on a star/delta setup
Is this the case...:confused:

Also be careful when selecting type of MCB or HRC fuse protecting a motor circuit.... due to start up / high inrush current.
 
Last edited:

Reply to star delta starter in the Electricians' Talk | All Countries area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock