Discuss TT System High Ze leading to possible Zs fails in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system, Diesel Generator that runs and charges batteries when they are below 10 percent or so.

Ra is about 150 Ohms... was about 3 ohms for Ze before main earth was disconnected from electrode.

Now table 53.1 tells me that a 500mA RCD would be acceptable in this instance, not that that would ever be the case as everything is protected by 30mA RCD albeit one main one for everything. ( An exception to this is the circuit from generator to Invertor IN circuit and Invertor OUT i don't believe is on an RCD. Invertor out is a 25A MCB which limits the entire supply which is a second 2 way DB in the shed that house the generator doing 2 sockets and then onto an 8 way main RCD board in the house.

My question is basically most mcbs 20 amp and above are failing max Zs readings ( In most instances not by much ).

Because it is a remote holiday let it has a very small amount of sockets and no kettle or any other appliances supplied and all heating cooking is gas/oil. I maybe have the luxury of sticking a couple of rings onto 10A mcbs in which case they pass but not sure if table 53.1 negates the need for this?

SO long as the RCD trips within 200ms can this be passed so long as deviations from BS7671 are noted?

Example readings are 16A MCB 2.5 Ohms which is 2.2 max and 32A MCB 3.5 Ohms which is 1.1 max. all other 6A circuits pass.

Appreciate advice as its not something i have dealt with too much over the years.

( Sorry for waffling on also cheers! )
 
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system, Diesel Generator that runs and charges batteries when they are below 10 percent or so.
I think you might have a TN-S system, the earth rod for the generator being the first T in TN-S not the second T in TT.
My question is basically most mcbs 20 amp and above are failing max Zs readings ( In most instances not by much ).
Well as Zs is the resistance of the circuit added to Ze, this is to be expected. So it comes down to considering line-earth faults at each point in the setup and working out what would happen (or not happen).

In my mind this boils down to:
1) confirming the generator earthing arrangements.
2) what is the type and rating of the fuse / device protecting the generator output
3) will a fault to earth before the first RCD clear and how long will it take
4) Is there 30ma RCD protection for every final circuit

Also, it may be that the generator output can be treated as a distribution circuit for disconnection time purposes.
 
If the installation is being fed from a small generator or an inverter then, regardless of the Zs, the supply will not be capable of delivering enough fault current to achieve disconnection times.

If an earth fault occurs it is likely that the generator's engine would stall due to the sudden additional load before any fuse or MCB operates.

The generator should incorporate the necessary protection for it's output, this may not be obvious though as it can be built in to the internal control system.
 
If the installation is being fed from a small generator or an inverter then, regardless of the Zs, the supply will not be capable of delivering enough fault current to achieve disconnection times.

If an earth fault occurs it is likely that the generator's engine would stall due to the sudden additional load before any fuse or MCB operates.

The generator should incorporate the necessary protection for it's output, this may not be obvious though as it can be built in to the internal control system.
Thanks for the reply mate, in normal operation the batteries/invertor would be supplying the installation so the generator stalling wouldn't stall as such. I think another visit to have a look at the invertor itself and inspect whether its control system offers any fault protection may be an idea?
 
I think you might have a TN-S system, the earth rod for the generator being the first T in TN-S not the second T in TT.

Well as Zs is the resistance of the circuit added to Ze, this is to be expected. So it comes down to considering line-earth faults at each point in the setup and working out what would happen (or not happen).

In my mind this boils down to:
1) confirming the generator earthing arrangements.
2) what is the type and rating of the fuse / device protecting the generator output
3) will a fault to earth before the first RCD clear and how long will it take
4) Is there 30ma RCD protection for every final circuit

Also, it may be that the generator output can be treated as a distribution circuit for disconnection time purposes.
Cheers for the quick response I appreciate it. Yes I believe you are right and it is infact TN-S... in my head the earth electrode automatically meant TT but i have little experience of dealing with them and have spent a bit of time reading up.

I am going to go back out a look this week but I believe it was a C40 double pole MCB on the generator itself.

May need some advice on point 3 and all final circuits have 30ma RCD.

Generator to Invertor and Invertor to sub mains are not RCD protected I don't believe but I'm gonna have a proper study when i get back.
 
I am going to go back out a look this week but I believe it was a C40 double pole MCB on the generator itself.

Often the generator MCB will have a shunt trip fitted so that the generator control panel can trip it should there be a fault. What make and model of generator is it? There may be earth leakage protection built in that isn't obvious at first due to it being inside the control panel.
 
Often the generator MCB will have a shunt trip fitted so that the generator control panel can trip it should there be a fault. What make and model of generator is it? There may be earth leakage protection built in that isn't obvious at first due to it being inside the control panel.
Cheers Dave,

Haven't made it back out as of yet.... it really is the back of beyond but i will get passed this coming week and find that out.
 
Often the generator MCB will have a shunt trip fitted so that the generator control panel can trip it should there be a fault. What make and model of generator is it? There may be earth leakage protection built in that isn't obvious at first due to it being inside the control panel.
Hi Dave the generator is a Lister Pelter T series nameplate 20001074TR2A08. Im not sure is there is earth leakage built in as of yet either but would I be right in saying that if it is charging batteries via the invertor then it would be the inverter that would need to have fault protection?

The invertor is a Outback Power VFX3024F single-phase Sine-Wave Invertor/Charger with 30 Amps AC Transfer switch.

There are 9 ( I believe and will confirm ) Rolls battery engineering Deep Cycle Series 4000 S-5550 Batteries in the system ( 6- Volt )

Appreciate the help for you guys on here as its not the type of thing I have a lot of experience with but interested to lay more about.

This particular issue is on a bit of a time scale and getting a bit of pressure but I won't sign to off until I have a better understanding of what is installed is safe.
 
Sounds to me as though this is a barrel of monkey's. You may have either a TN or floating earth from the generator, depending on size and quality and then again either a created TN or possibly even IT from the invertor.

Neither of these, as others have said, is likely to be able to produce enough raw energy to produce sufficient pfc for ADS, so your Ra is all but irrelevant. However, if all final circuits are protected by 30mA RCD then your max allowable Zs becomes the magic 1667Ω.
Ultimately in these situations what you're having to make a decision on is whether something is safe, not that it complies with scenarios never considered years ago. Engineering sense would suggest that the simplest way to make the system safe would be to contemplate making the whole situation IT - however frustratingly that's one thing you can't do according to BS7671 unless it's under supervision.

What I would say is that for this reason the vast majority of invertors have some very clever fault sensing circuitry within them to allow for these situations which makes both an overload situation unlikely and you have final cct protection via RCD's to limit touch voltages for humans. It can be very easy to go down a rabbit hole of overthinking things!

133.5 "Where the use of a new material or invention leads to departures from the Regulations, the resulting degree of safety of the installation shall not be less than that obtained by compliance....."
 
You may have either a TN or floating earth from the generator, depending on size and quality and then again either a created TN or possibly even IT from the invertor.
In this case the inverter isn't IT, N is passed straight through it.
So whatever earthing the generator is will also apply to the inverter output.
1694602951005.png


Also of note is:
1694602554100.png

So hopefully the installation earth isn't only connected to the ground terminal of the inverter.
It's clear from the manual that the inverter is clever and can be configured to not overload a generator and disconnect the output if too much is drawn.

( https://www.energymatters.com.au/images/outback/FX-VFX-Manual.pdf )

With final circuits RCD protected, I'm struggling to see real-life issues with this setup.
 

Reply to TT System High Ze leading to possible Zs fails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
504
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Cable calcs using cable calc app Working out cable size for a workshop. 100m long, 100a supply, mccb 100a zs- 0.23 ohms, in a duct on its own...
Replies
2
Views
1K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
827

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock