I've just installed my first Zappi.

The customer just wants to plug in the vehicle and is not fussed about WiFi connection. I have checked with Myenergi and the Zappi can run without the need to be connected to the net. However, when I plug the car in it comes up with 'Check CT grid' and will not charge. I cant contact Zappi today as its the bank hol. Just wondered if anyone has had this? Perhaps @Gavin John Hyde ?

Is it anything to do with the use of a CT clamp? I have not installed one as it is a 100a fuse and well within max demand.
 
Its default is having CT clamp connected, you need to go into settings and disable CT
Page 27 of manual, just done one and was a eye brow raise as previous ones did not default to grid CT
Thanks for that.
I've just been looking at p.27 and it talks mainly about the e-sense. where abouts does it mention disabling the CT? Have attached t he manual I am reading in case they are different.
 

Attachments

  • Zappi-2-Full-Manual-V1_6.pdf
    3.8 MB · Views: 55
in the menus for ct settings ct1 is set as default to on and grid ct. with the ct clamp not being connected you need to go back to charger or talk customer through steps and turn ct1 off, then charger wont be looking for the grid ct, at moment its basically open circuit
 
go into menus, go to advanced enter code 0000 (assuming its not changed) go to ct config, leave the ct int alone as that is the internal one for charging. for ct1 ct2 and ct3 go into each and use the arrow keys to turn to off. this will resolve the problem. zappis have ct1 on as default as they encourage/assume the ct will be fitted.
quite quick and easy and take less than 30secs so you could talk customer through steps. I have got a customer to add a harvi and extra ct for his solar into his zappi over the phone before and he wasnt the most clued up of people with technology
 
go into menus, go to advanced enter code 0000 (assuming its not changed) go to ct config, leave the ct int alone as that is the internal one for charging. for ct1 ct2 and ct3 go into each and use the arrow keys to turn to off. this will resolve the problem. zappis have ct1 on as default as they encourage/assume the ct will be fitted.
quite quick and easy and take less than 30secs so you could talk customer through steps. I have got a customer to add a harvi and extra ct for his solar into his zappi over the phone before and he wasnt the most clued up of people with technology
That's really helpful Gavin, thankyou 🙂
 
go into menus, go to advanced enter code 0000 (assuming its not changed) go to ct config, leave the ct int alone as that is the internal one for charging. for ct1 ct2 and ct3 go into each and use the arrow keys to turn to off. this will resolve the problem. zappis have ct1 on as default as they encourage/assume the ct will be fitted.
quite quick and easy and take less than 30secs so you could talk customer through steps. I have got a customer to add a harvi and extra ct for his solar into his zappi over the phone before and he wasnt the most clued up of people with technology
It worked exactly as you said Gavin.

I could have rang Zappi, which means I could have spent 30 minutes getting through, and then been met with someone who had no idea how to fix the problem, meaning a call back hours later by someone else.

Really appreciate all the help you give regarding EVCP Gavin. It may not seem much to you that little bit of advice you gave above, but It may well have saved me quite a bit of waiting.

I shall know for next time!
 
go into menus, go to advanced enter code 0000 (assuming its not changed) go to ct config, leave the ct int alone as that is the internal one for charging. for ct1 ct2 and ct3 go into each and use the arrow keys to turn to off. this will resolve the problem. zappis have ct1 on as default as they encourage/assume the ct will be fitted.
quite quick and easy and take less than 30secs so you could talk customer through steps. I have got a customer to add a harvi and extra ct for his solar into his zappi over the phone before and he wasnt the most clued up of people with technology
Many thanks for your answer, turned CT1 off and now able to charge.
 

Reply to What does 'Check CT grid' mean on zappi EVCP install? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top