Which rcd type do you use for general use in your country?

Discuss Which rcd type do you use for general use in your country? in the UK Electrical Forum area at ElectriciansForums.net

In the UK the law does not specify the electrical details, but it does state the meeting the IET wiring regulations BS 7671 ought to achieve compliance. Yes, it appears odd to begin with but it allows for the technical standards to evolve and be interpreted without needing legal oversight.

In turn that cites various other standards specifically describing RCDs as one of several means of protection against electric shock (and fire in some cases) such as BS EN 61008-1 and BS EN 61009-1 and others.

It is common for RCDs to be of the 'AC' type that is only good on an AC leakage current, but many manufactures are moving to type A as standard (pulsed DC sensitivity, as required by many European countries) and occasionally you will see type B (true DC) or F (also HF noise).

Certainly I would not use a type AC in any setup if there was any alternative!
[automerge]1588536524[/automerge]
A quick overview aimed at electricians and consumers can be found here:

Just follow the download link!
 
Last edited:

Reply to Which rcd type do you use for general use in your country? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top